Also
There is a meter study which created changes in the 2013 NFPA 13D. (see a below)

http://www.nfpa.org/research/fire-protection-research-foundation/rss-feed-items/home-fire-sprinklers/residential-fire-sprinklers

(4)*Pressure loss for a water meter, if any, shall be determined
and deducted using one of the following:
(a) Table 10.4.3(a) shall be permitted to be used, even
where the sprinkler demand flow exceeds the
meter's rated continuous flow.
(b) Higher pressure losses specified by the manufacturer
shall be used in place of those specified in
Table 10.4.3(a).
(c) Lower pressure losses shall be permitted to be used
where supporting data are provided by the meter
manufacturer.


Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



We're hiring great people at all of our locations!  Please check out our 
website for the details! 




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Monday, August 03, 2015 6:22 PM
To: [email protected]
Subject: RE: Old dog, new tricks?

I guess we get credit for a pretty thoughtful effort then.  We also amended the 
code to require sprinklers in garages and traded down the least allowable 
setbacks to give developers the potential for higher densities that could 
generate additional revenues from parcels that could subsidize the added costs 
of sprinklers in general.   To make the garage sprinklers palatable, we waived 
the requirement for a fire-rated door and rated sheetrock on the vertical 
surfaces (those exemptions offset more than the cost of the garage sprinklers). 
  We made one important condition to the exemptions:  sheetrock on the lid 
between a garage or carport with living space over must still be sprinklered.   
So with some foresight, you head off the local restrictive amendments, which 
was our goal:  create a modified standard that local AHJ's weren't tempted to 
modify.   And to the AHJ who decided that you should use 13 on an attached SFD 
garage ... well, sorry if this sounds disrespectful but that's just ludicrous.  
  

To the 5 GPM and water meter sizes, we also partnered with ACWA - the 
Association of California Water Agencies.   They agreed to establish BMP's for 
sprinklered homes and one of the considerations was to overlook the 5 GPM.   
Here's the back-story on meters, y'all:

Water meters are for measuring water.  Their maximum flow ratings are for no 
more than 2% error in the reading of consumption.   That is NOT the maximum 
amount of water you can flow through them, it's the maximum CONTINUOUS FLOW (as 
in 24/7) that you can flow at no worse than 98% accuracy.   Meters can tolerate 
dozens of GPM more flow without damage, but they are rated to 98% accuracy.   
Flow at maximum calculated demand is, hopefully, a once-in-a-lifetime even so 
it's considered an INTERMITTENT FLOW.   So it's really not a reach to size your 
meter for the 26 or 28 or 32 or 36 or 40 GPM that various sprinklers would 
require in 2-sprinkler design areas at different areas of coverage and then add 
a "virtual" 5 GPM to the calculation.   You obtain an accurate head loss and if 
it should ever operate in a fire, the water purveyor accepts that the meter 
might not measure the sprinkler flow for billing purposes in an intermittent 
flow event.   

On top of that, look into meters rated for higher than class average flows.  
Badger makes a series of meters called Recordall:  they offer a ¾" rated at 25 
GPM continuous and 35 GPM intermittent.   They make a 1" rated at 40/55 and 
another 1" rated 50/70.  Yes, manufacturer rated at 70.   So ... let's all stop 
being victims and start shoving information down the throats of the uneducated 
and the naysayers.   Several years ago, I brokered a meeting between a city 
water department, two large homebuilders and a sprinkler contractor.  The city 
was insisting that they use 1" meters at an additional cost of $5,000 per lot 
on two subdivisions consisting of 440 lots.   $2.2M in capacity fees.  I 
performance-engineered a solution that utilized 3/4" meters that addressed the 
sprinkler flows AND The concurrent 5 GPM allowance and saved the developers 
those costs.  To my deepest regret, I did not get compensated on a % of savings 
basis.  However, I am available for consulting on a fee simple basis + expenses.

Steve                   






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Monday, August 03, 2015 10:39 AM
To: [email protected]
Subject: Re: Old dog, new tricks?

Steve,

California already has their universal ordinance requiring sprinklers.
Modification to provide better protection is then a good idea. But what if that 
5gpm generally requires a larger meter where the water purveyor is still 
charging commercial meter rates and the bill goes up bunches? There's a 
jurisdiction here that decided that garages need sprinkle ring and without 
guidelines went to 13. Residential garages now need to be sprinklered there as 
if they were S2 occupancies as an Ord 1 hazard. Better heat the thing too so 
you don't need a dry system. This does not help get a statewide ordinance 
passed.

On Mon, Aug 3, 2015 at 10:27 AM, Steve Leyton <[email protected]>
wrote:

>
>
> It's a universal requirement in CA. Code amendments ...
>
> Steve
>
> -------- Original message --------
> From: "rongreenman ." <[email protected]>
> Date: 08/03/2015  10:24 AM  (GMT-08:00)
> To: [email protected]
> Subject: Re: Old dog, new tricks?
>
> Not required at all by 13D as far as I know. This seems to be another 
> one where the local AHJ is making things up based on a hunch. Although 
> adding a 10% cushion, 5gpm for domestic, heads in an attic or garage 
> might be better fire protection, particularly for property protection, 
> adding cost to13D systems defeats the purpose of 13D, which is to 
> provide an adequate degree of survivability for a few extra minutes 
> for people, not the building at a minima cost. It's hard enough to 
> convince legislative bodies that these systems are a good investment without 
> adding things that are unnecessary.
> AHJs are supposed to alter basic requirements, where they are allowed 
> to do so, based on special jurisdictional needs. I doubt that this 
> particular community has something going on that suggests domestic 
> usage is so much higher than average that people will die unless a 
> domestic demand is included in the calcs.
>
> On Mon, Aug 3, 2015 at 8:34 AM, Travis Mack, SET <[email protected]>
> wrote:
>
> > Only in certain jurisdictions where they require we add 5gpm, or 
> > where we have a duplex.
> >
> > Travis Mack, SET
> > MFP Design, LLC
> > 2508 E Lodgepole Drive
> > Gilbert, AZ 85298
> > 480-505-9271
> > fax: 866-430-6107
> > email:[email protected]
> >
> > http://www.mfpdesign.com
> > https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> > Send large files to us via: https://www.hightail.com/u/MFPDesign
> >
> >
> > On 8/3/2015 8:32 AM, Vince Sabolik wrote:
> >
> >> Does anyone account for domestic water use in calculations for a 
> >> typical 13D one family system?
> >>
> >> Curious + woof!
> >>
> >>
> >>                                              thanks, Vince
> >>
> >>
> >>
> >> West Tech Fire Protection, Inc.
> >> 11351 Pearl Road   / Strongsville, Ohio   44136
> >> Phone 440 238-4800    Fax 440 238-4876   Cell  440 724-7601
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> >>
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis 
> Bacon, essayist, philosopher, and statesman (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F. Kettering, 
> inventor and engineer (1876-1958) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to