Owen,

It comes down to a building code issue. I recently completed a project such
as you describe. Initially, it was "ruled" as 13D by the fire department.
Then the building officials indicated that the architect had taken several
sprinkler exceptions such as height, access road width, etc. These variances
bumped the system from 13D to 13R. I'd recommend making some phone calls. 

Marc Walter, SET
Sprinkler Design Services
780 6th Avenue
Seaside, OR  97138
(503) 956-4019



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Owen Evans
Sent: Tuesday, September 01, 2015 11:00 PM
To: [email protected]
Subject: 13D installed in Townhouse?


The definition on townhouse is a one-family dwelling constructed in attached
groups of three or more units in which each unit extends from the foundation
to the roof and has open space on at least two sides.


Question:
Does that mean if you had five attached townhouses you can install 13D
system in each unit (each having a system riser with flow switch and bell),
with all five townhouses being supplied off of one water meter (five risers
being served by one meter) with the most remote/demanding unit being
calculated per 13D, 2 heads flowing?  In other words, each unit has it's own
water meter supplying domestic needs, with a sixth, stand alone water meter,
supplying all six townhouses 13D system?  Yes or NO?


Or 


Does that mean each unit, because they are attached but separated foundation
to roof, can have a 13D system, each being supplied off its own domestic
water meter? 


Owen Evans

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6125 / Virus Database: 4409/10558 - Release Date: 09/01/15

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to