First off what does this mean? What kind of test? That the batteries hold a
charge for this duration? That the batteries don't turn into pumpkins at
midnight? That the batteries can hold a charge and still operate the SLC.
The only duration I can find in 72-2013 that even remotely relates to
suppression systems are the same that apply to panels. In a protected
premise 24 hours of standby followed by five minutes of full load operation
or fifteen minutes if there is voice evacuation. Maybe I'm looking for love
in the wring place but it seems to me that if the release relay operates
between 24 hours and 24 hours plus five minutes then you've met the
criteria.

On Fri, Oct 23, 2015 at 11:11 AM, Easter, Timothy <[email protected]>
wrote:

> Is there an actual requirement during acceptance testing of foam systems
> to conduct a 72 or 90 hour battery test on the Foam panel and the foam
> controllers, if so where is the information located?  I have a contractor
> telling me its required.
>
> Feel free to contact me with any questions.
> Regards,
>
> Timothy Easter, E.I.T.
> Graduate Fire Protection Engineer
> Direct: (757) 383-6217
> [email protected]<mailto:[email protected]>
>
> AECOM
> 11832 Rock Landing Drive Suite, 306, Newport News, Virginia 23606
> www.aecom.com
>
>
>
> This e-mail and any attachments contain AECOM confidential information
> that may be proprietary or privileged. If you receive this message in error
> or are not the intended recipient, you should not retain, distribute,
> disclose or use any of this information and you should destroy the e-mail
> and any attachments or copies.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to