First off what does this mean? What kind of test? That the batteries hold a charge for this duration? That the batteries don't turn into pumpkins at midnight? That the batteries can hold a charge and still operate the SLC. The only duration I can find in 72-2013 that even remotely relates to suppression systems are the same that apply to panels. In a protected premise 24 hours of standby followed by five minutes of full load operation or fifteen minutes if there is voice evacuation. Maybe I'm looking for love in the wring place but it seems to me that if the release relay operates between 24 hours and 24 hours plus five minutes then you've met the criteria.
On Fri, Oct 23, 2015 at 11:11 AM, Easter, Timothy <[email protected]> wrote: > Is there an actual requirement during acceptance testing of foam systems > to conduct a 72 or 90 hour battery test on the Foam panel and the foam > controllers, if so where is the information located? I have a contractor > telling me its required. > > Feel free to contact me with any questions. > Regards, > > Timothy Easter, E.I.T. > Graduate Fire Protection Engineer > Direct: (757) 383-6217 > [email protected]<mailto:[email protected]> > > AECOM > 11832 Rock Landing Drive Suite, 306, Newport News, Virginia 23606 > www.aecom.com > > > > This e-mail and any attachments contain AECOM confidential information > that may be proprietary or privileged. If you receive this message in error > or are not the intended recipient, you should not retain, distribute, > disclose or use any of this information and you should destroy the e-mail > and any attachments or copies. > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org