Are you questioning the hours of standby time required or the test method to 
disconnect primary power for the required time and test the system at the end 
for require duration.  

Military foam is 48 standby and 15 in alarm.  I have seen places a little more 
remote require longer than 48 and honestly it's justified in many cases.  Take 
an island and a typhoon.  Take a site a long way off the main grid. Could be a 
long time to get things back up and running. Losing the fire alarm is one 
thing, losing the fire suppression is a bigger thing IMHO. Many people die in 
buildings with fire alarms but nearly none in buildings with fire suppression. 

Testing to those conditions is supported in NFPA 72 Table 14.4.3.2 item 7:

"Disconnect all primary (main) power supplies and verify the occurrence of 
required trouble indication for loss of primary power. Measure or verify
the systems standby and alarm current demand and verify the ability of 
batteries to meet standby and alarm requirements using manufacturer's
data."

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Easter, Timothy
Sent: Friday, October 23, 2015 1:11 PM
To: [email protected]
Subject: 72 or 90 hour battery test on the Foam panel and the foam controllers

Is there an actual requirement during acceptance testing of foam systems to 
conduct a 72 or 90 hour battery test on the Foam panel and the foam 
controllers, if so where is the information located?  I have a contractor 
telling me its required.

Feel free to contact me with any questions.
Regards,

Timothy Easter, E.I.T.
Graduate Fire Protection Engineer
Direct: (757) 383-6217
[email protected]<mailto:[email protected]>

AECOM
11832 Rock Landing Drive Suite, 306, Newport News, Virginia 23606 www.aecom.com



This e-mail and any attachments contain AECOM confidential information that may 
be proprietary or privileged. If you receive this message in error or are not 
the intended recipient, you should not retain, distribute, disclose or use any 
of this information and you should destroy the e-mail and any attachments or 
copies.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to