Exactly. The paragraph for sprinkler piping is there as the only one permitted. I have switched to a sleeve around the penetration pipe extending past the "dedicated space". This satisfies the requirement in most places. I do not believe in shields as they obstruct water. After all, what if it is the panel on fire.
R/ Matt -----Original Message----- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Amanda Brown Sent: Friday, October 30, 2015 5:43 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: sprinkler pipe passing through electrical rooms Can you run pipe "through" and electrical room... yes. It is standard practice to terminate at a head and not continue through the room due to AHJ interpretation. Concerns: 1. Electrical Panels - You can't run pipe directly over the panel, in the space from the top of the panel to 6'-0" above the top of the panel. A pipe can be higher than that only if there is a drip plate/shield, etc. between the pipe and the panel. (NEC110.26(F)) 2. Working Space - See NEC 110.26 The truth of this code is.... ask the AHJ - because regardless what your interpretation is, this one is touchy and AHJ's have their mind made up whether pipe can or cannot enter and exit an electrical room. A. Brown Fire Protection Designer 13504 South Point Blvd, Suite M | Charlotte, NC 28273 EMAIL: abr...@goipi.com TEL: 704-588-1100 x 602 MOBILE: 919-931-1075 WEB: www.ipifireprotection.com -----Original Message----- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Greg McGahan Sent: Friday, October 30, 2015 6:45 AM To: sprinklerfo...@firesprinkler.org Subject: sprinkler pipe passing through electrical rooms Am I mis-remembering that somewhere in some code - 13 or 70 - that there used to be a statement that dictated that the only sprinkler pipe allowed in an electrical room was the pipe feeding sprinklers in the room? Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org