Exactly. The paragraph for sprinkler piping is there as the only one permitted.
I have switched to a sleeve around the penetration pipe extending past the 
"dedicated space". This satisfies the requirement in most places.
I do not believe in shields as they obstruct water.  After all, what if it is 
the panel on fire.

R/
Matt

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Amanda Brown
Sent: Friday, October 30, 2015 5:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: sprinkler pipe passing through electrical rooms

Can you run pipe "through" and electrical room... yes.  It is standard practice 
to terminate at a head and not continue through the room due to AHJ 
interpretation.

Concerns:

1.  Electrical Panels - You can't run pipe directly over the panel, in the 
space from the top of the panel to 6'-0" above the top of the panel.  A pipe 
can be higher than that only if there is a drip plate/shield, etc. between the 
pipe and the panel.  (NEC110.26(F))

2.  Working Space - See NEC 110.26

The truth of this code is.... ask the AHJ - because regardless what your 
interpretation is, this one is touchy and AHJ's have their mind made up whether 
pipe can or cannot enter and exit an electrical room.

A. Brown
Fire Protection Designer
13504 South Point Blvd, Suite M | Charlotte, NC  28273
EMAIL:  abr...@goipi.com 
TEL:  704-588-1100 x 602
MOBILE: 919-931-1075
WEB:  www.ipifireprotection.com

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Greg McGahan
Sent: Friday, October 30, 2015 6:45 AM
To: sprinklerfo...@firesprinkler.org
Subject: sprinkler pipe passing through electrical rooms

Am I mis-remembering that somewhere in some code - 13 or 70 - that there used 
to be a statement that dictated that the only sprinkler pipe allowed in an 
electrical room was the pipe feeding sprinklers in the room?

Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to