The situation I was dealing with is not a rack.  It is a shelf - solid back, 
solid shelves, solid ends.  It is not likely to get a full scale test for a 
not-all-that-common setup.  Or maybe it is more common than I think.  

John F. Hoffman, PE*  \  Burns & McDonnell
Senior Fire Protection Engineer
O 816-349-6759 \  M 816-255-4102 
[email protected]  \  burnsmcd.com
9400 Ward Parkway  \  Kansas City, MO 64114

Proud to be one of FORTUNE's 100 Best Companies to Work For
Please consider the environment before printing this email.
*Registered in: MO

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott Futrell
Sent: Thursday, October 29, 2015 4:36 PM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

Hmmm...John that is interesting direction you are giving there.

Do you have NFPA 13 or full-scale testing to support the "ESFR could spray 
below the catwalk" comment? Or, that OH2 below the catwalk will not allow the 
fire to grow horizontally along the racking overwhelming the ESFR above?

If the catwalk doesn't extend through the rack how can you protect a 30' high 
(or pick a height) rack storage with QR sprinklers below the catwalk level and 
ESFR above the catwalk level when it's all the same rack storage from the 
ground up with flue spaces open and continuous to the roof.  I must be missing 
something here.

I assume the direction of the catwalk would/could enter into the scenario, but 
I would like to see your support for the comments you've made here, and if you 
have that support great!

Scott
 
Office: (763) 425-1001 x 2
Cell: (612) 759-5556


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John F Hoffman
Sent: Thursday, October 29, 2015 4:14 PM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

If the roof-level ESFR could spray below the catwalk (assuming open grating) 
you would not need the sprinklers under the catwalk.  But, as mentioned before, 
you are forced to put a cover on the grating so should be able to install 
whatever sprinklers can deal with the hazard under the grating.

Class IV shelf storage up to 12 feet high can be protected with OH2.   Even 
plastic shelf storage only requires EH1 or EH2 depending on height.   ESFR is 
overkill.  

John F. Hoffman, PE*  \  Burns & McDonnell Senior Fire Protection Engineer O 
816-349-6759 \  M 816-255-4102 [email protected]  \  burnsmcd.com
9400 Ward Parkway  \  Kansas City, MO 64114

Proud to be one of FORTUNE's 100 Best Companies to Work For Please consider the 
environment before printing this email.
*Registered in: MO





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to