2013 & 2016 editions no longer require calculating 2 additional ESFR's under 
obstructions.

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Friday, October 30, 2015 2:24 PM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

Put ESFR's under the catwalk and include two (2) additional ESFR's in the 
calc's total of fourteen heads flowing.
Just like it's an obstruction.

Mike

> From: [email protected]
> To: [email protected]
> Subject: RE: ESFR Sprinklers and covered catwalks
> Date: Fri, 30 Oct 2015 18:16:25 +0000
> 
> The situation I was dealing with is not a rack.  It is a shelf - solid back, 
> solid shelves, solid ends.  It is not likely to get a full scale test for a 
> not-all-that-common setup.  Or maybe it is more common than I think.  
> 
> John F. Hoffman, PE*  \  Burns & McDonnell Senior Fire Protection 
> Engineer O 816-349-6759 \  M 816-255-4102 [email protected]  \  
> burnsmcd.com
> 9400 Ward Parkway  \  Kansas City, MO 64114
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For Please 
> consider the environment before printing this email.
> *Registered in: MO
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Scott Futrell
> Sent: Thursday, October 29, 2015 4:36 PM
> To: [email protected]
> Subject: RE: ESFR Sprinklers and covered catwalks
> 
> Hmmm...John that is interesting direction you are giving there.
> 
> Do you have NFPA 13 or full-scale testing to support the "ESFR could spray 
> below the catwalk" comment? Or, that OH2 below the catwalk will not allow the 
> fire to grow horizontally along the racking overwhelming the ESFR above?
> 
> If the catwalk doesn't extend through the rack how can you protect a 30' high 
> (or pick a height) rack storage with QR sprinklers below the catwalk level 
> and ESFR above the catwalk level when it's all the same rack storage from the 
> ground up with flue spaces open and continuous to the roof.  I must be 
> missing something here.
> 
> I assume the direction of the catwalk would/could enter into the scenario, 
> but I would like to see your support for the comments you've made here, and 
> if you have that support great!
> 
> Scott
>  
> Office: (763) 425-1001 x 2
> Cell: (612) 759-5556
> 
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> John F Hoffman
> Sent: Thursday, October 29, 2015 4:14 PM
> To: [email protected]
> Subject: RE: ESFR Sprinklers and covered catwalks
> 
> If the roof-level ESFR could spray below the catwalk (assuming open grating) 
> you would not need the sprinklers under the catwalk.  But, as mentioned 
> before, you are forced to put a cover on the grating so should be able to 
> install whatever sprinklers can deal with the hazard under the grating.
> 
> Class IV shelf storage up to 12 feet high can be protected with OH2.   Even 
> plastic shelf storage only requires EH1 or EH2 depending on height.   ESFR is 
> overkill.  
> 
> John F. Hoffman, PE*  \  Burns & McDonnell Senior Fire Protection 
> Engineer O 816-349-6759 \  M 816-255-4102 [email protected]  \  
> burnsmcd.com
> 9400 Ward Parkway  \  Kansas City, MO 64114
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For Please consider 
> the environment before printing this email.
> *Registered in: MO
> 
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to