Dedicated Space and Working Space.  The two distinct spaces within and around 
electrical equipment with special rules.

Dedicated is above, Working is in front.

Agreed, this is one of several areas where there is confusion. You have to do 
some digging outside of NFPA 13 for the correct answers.

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, November 05, 2015 11:08 AM
To: [email protected]
Subject: RE: sprinkler pipe passing through electrical rooms

It strikes me now that many may confuse "dedicated electrical space" for an 
entire electrical room, not just the spaces in front of or above electrical 
panels.

Just like many confuse rules for transformer vaults with those for average 
electrical rooms.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, November 04, 2015 11:59 AM
To: [email protected]
Subject: RE: sprinkler pipe passing through electrical rooms

Yes, there is a big difference in providing protection for the dedicated 
electrical space and running your sprinkler pipes within the dedicated 
electrical space.

Sprinklers are permitted to spray water into the dedicated electrical space as 
noted, just keep the pipes and sprinklers themselves outside the boundary 
limits of the space.

Craig L. Prahl
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Frank Herrick
Sent: Wednesday, November 04, 2015 11:48 AM
To: '[email protected]' 
<[email protected]>
Subject: RE: sprinkler pipe passing through electrical rooms

Just found this is in consulting-specifying engineer magazine (6/20/2014)

Question: My jurisdiction is still under the 2008 NEC. Sprinklers are not 
permitted in the dedicated electrical equipment space. What code edition does 
this change to be allowable per the slide presented?

The 2014 NEC allows sprinkler protection for the dedicated space, not 
specifically that the piping can run in the dedicated space. Please refer to 
our example diagram in the presentation. The NEC states that the sprinkler 
protection must comply with the other portions of 110.26(E). This provision is 
in the 2008 NEC as well.

Captain Frank J. Herrick
City of Leawood Fire Department

-----Original Message-----
From: Greg McGahan [mailto:[email protected]]
Sent: Friday, October 30, 2015 5:45 AM
To: [email protected]
Subject: sprinkler pipe passing through electrical rooms

Am I mis-remembering that somewhere in some code - 13 or 70 - that there used 
to be a statement that dictated that the only sprinkler pipe allowed in an 
electrical room was the pipe feeding sprinklers in the room?

Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to