How do you mess up:

8.3.2.1 Unless the requirements of 8.3.2.2, 8.3.2.3, 8.3.2.4, or 8.3.2.5 are 
met, ordinary and intermediate-temperature sprinklers shall be used throughout 
buildings.

Intermediate can be used throughout unless other sections require a different 
temperature rating.

Duane Johnson, PE
Design Manager
Strickland Fire Protection
5113 Berwyn Road
College Park, MD 20740
301-474-1136 Office
301-455-0010 Cell


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Thursday, November 12, 2015 10:53 AM
To: [email protected]
Subject: Intermediate temperature sprinklers

We are designing an apartment complex per NFPA 13 requirements.  Is it 
permissible to install intermediate temperature sprinklers throughout all 
spaces (except those that would specifically require a high temp sprinkler due 
to other sections)?

The specific question arises because we have ordinary temperature sprinklers 
throughout most areas, and intermediate temp sprinklers in mechanical closets 
and laundry rooms in the dwelling units.  The AHJ states that since the areas 
(mech closets and laundry areas in the dwelling units) are conditioned spaces, 
that we must use ordinary temperature rated sprinklers.  He states that Table 
8.3.2.5(c) over-rides the flexibility provided by 8.3.2.1 which allows ordinary 
or intermediate temp sprinklers throughout buildings.

This has been common practice to install the intermediate temp sprinklers in 
these areas.  This is the first time that this plan reviewer has ever brought 
this up.  Some contractors in this area are moving toward intermediate temp 
sprinklers throughout in residential areas for various reasons.

-- 
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to