Matt,

Yes, I agree with the point of not taking on responsibility, that is why I am 
trying to find a way to point to a published standard for our design choice.  
Yes we are also looking into FM standards as well for other possible design 
solutions.  

I guess I'm more pointing out that the wording of this section seems silly or 
lacking, and wondering if anyone else has run into this or if there should be 
an item #11 added that states "also usable in open racks".  The handbook talks 
about how slatted shelves should be treated as solid shelves, hence why I 
believe they added this section.  Since we can't use solid shelves with ESFR 
but fire tests showed slatted shelves work under very specific conditions.  So 
taking it one step further, this design concept is for using slatted shelves, 
which is a worse storage arrangement compared to open racks, the design 
criteria should therefore be useable for open racks...Right?  But I do not see 
a clear path for using K25 @ 15psi with open racks, even if all other line 
items are the same.  So in essence, the way I read it, I build the racks and 
store the commodity exactly as 17.2.4 states and NFPA says fire tests proved 
this it works so we are good with it.  I take out the slatted shelves and NFPA 
says we have no fire tests to prove this, so use K16 @ 35psi or K25 @ 50psi.  
How does that make sense?

Thanks,
Sean VG





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Thursday, November 12, 2015 9:44 AM
To: [email protected]
Subject: RE: NFPA 13 plastics up to 25ft roof 30ft with K25 heads

I would not recommend using the adjustment you proposed. Without a very 
complete knowledge of how the sprinklers perform at various flows you are 
putting yourself in a risky position. 

If you can meet all of the special criteria of 17.2.4, then that should be 
fine. FM also has a design that uses k25.2 heads at 35psi.

You might also check the listing documents for the sprinklers you want to use. 
They sometimes are updated with new approved criteria that are not in 13 yet.

If you take on the responsibility of coming up with a new application for a 
product (in this case - k25.2's at 15.7psi) then you are also taking on a great 
deal of responsibility that it will work.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 
 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, November 12, 2015 10:28 AM
To: [email protected]
Subject: NFPA 13 plastics up to 25ft roof 30ft with K25 heads

Hi Forum,

The following is based on NFPA 13 (2013).  We have a roof height of 30ft, owner 
wants to store exposed unexpanded plastics in double row open racks up to 25ft. 
 No solid shelves or open top containers.  Looking at Table 17.2.3.1 my options 
are 14k@50psi OR 16.8k@35psi.  We have low water pressure and the owner doesn't 
want a fire pump, he also wants ESFR, so we want to use K25@15psi.  K25 doesn't 
come into play until storage is 25ft with a 40ft roof, but it requires 50psi.  
This pressure wouldn't work for what we are being asked to do.  Using our 
K-factor formula equation the K14 and K17 heads require roughly 100gpm based on 
this table.  If I run the K25 at 15.7psi I get 100gpm.  Does anyone see this as 
being a problem?  Is there an issue with the water not being able to penetrate 
the fire if the pressure is so low on a K25 while also being located so close 
to the top of the storage?

To make this extra confusing If we read through section 17.2.4, it appears it 
will allow me to use the K25@15psi so long as I meet the 10 requirements.  But 
this section is for when you want to use slatted shelves.  Which would seem to 
delay heat travel and water travel compared to open racks.  I'm sure I can 
convince the owner to follow these line an verse if he wants to do this storage 
arrangement, but it doesn't make sense to me that adding slatted shelves and 
wire mesh should be necessary.  Since it specifically doesn't state that open 
racks are also allowed with this design, I might run into a reviewer that is 
checking boxes rather than trying to think it through.

Thoughts?  Thank you for your time an help.

Thanks,
Sean VG





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to