Hi Forum, The following is based on NFPA 13 (2013). We have a roof height of 30ft, owner wants to store exposed unexpanded plastics in double row open racks up to 25ft. No solid shelves or open top containers. Looking at Table 17.2.3.1 my options are 14k@50psi OR 16.8k@35psi. We have low water pressure and the owner doesn't want a fire pump, he also wants ESFR, so we want to use K25@15psi. K25 doesn't come into play until storage is 25ft with a 40ft roof, but it requires 50psi. This pressure wouldn't work for what we are being asked to do. Using our K-factor formula equation the K14 and K17 heads require roughly 100gpm based on this table. If I run the K25 at 15.7psi I get 100gpm. Does anyone see this as being a problem? Is there an issue with the water not being able to penetrate the fire if the pressure is so low on a K25 while also being located so close to the top of the storage?
To make this extra confusing If we read through section 17.2.4, it appears it will allow me to use the K25@15psi so long as I meet the 10 requirements. But this section is for when you want to use slatted shelves. Which would seem to delay heat travel and water travel compared to open racks. I'm sure I can convince the owner to follow these line an verse if he wants to do this storage arrangement, but it doesn't make sense to me that adding slatted shelves and wire mesh should be necessary. Since it specifically doesn't state that open racks are also allowed with this design, I might run into a reviewer that is checking boxes rather than trying to think it through. Thoughts? Thank you for your time an help. Thanks, Sean VG _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org