I agree on the whole with Duane, but for a couple of clarifications to his 
statements that I'll hit on later. With over 40 years in the industry and 20 
years in special hazards here's my take: it is true, using different detection 
technologies and cross zoning them gives better assurance against false or 
unwanted activations. In most cases it is also true that this kind of setup 
will delay the activation of the valve. My question would be - is this 
critical, given that the water is not going to deploy until a head fuses?

Modern technology in detection and control systems provides a range of choices, 
I'll attempt to hit some highlights without getting long winded.  

In a setting where critical operations or artifacts are at risk we should as an 
industry do what we can to ensure suppression is employed only when needed, so 
double up on automatic detection via cross zone and even multiple technologies. 
Or, as Duane suggests use double interlock.

On the other hand, if protecting a generator enclosure an accidental dowsing of 
water is probably not going to be catastrophic; here single interlock on a 
single detector activation rather than cross zone works just fine. My practice 
has been to use heat detection in this setting and preferably flame detection 
as well. Sometimes these are cross zoned, sometimes not. Speaking to Steve's 
comment about incipient fires and their rate of growth, Class B fuels do not 
take long to woosh into fully involved; flame detection will give the quickest 
reaction for these fuels. 

Some will point out that flame detectors have caused them misery and pain due 
to false activations. The industry and technologies have come a long way from 
the first UV detectors (which caused me misery and pain back when) to the point 
that when properly applied they are very reliable.

I would also mention that for automatic smoke or heat detection used for 
suppression one should always reduce listed detector spacing by at least half, 
sometimes more depending on conditions.

Bottom line is that application of detection is application specific. Air 
sampling smoke detection is a great solution and provides lots of flexibility 
in design and implementation - I love it. Spot smoke detection works well but 
has challenges in high airflow or dirty environments. Heat detection is 
reliable but generally slower to respond unless the fire has moved beyond the 
incipient stage. 

As an aside, FMG's take on pre-action is to use heat detection and NOT cross 
zone; whether single or double interlock. 

As this is a technical forum I want to point out a couple misstatements in 
Duane's info. Nothing personal Duane, just sharing info. Firstly, ionization 
smoke detectors are no longer available from any of the system manufactures 
(hazmat disposal issues). Second, alarm verification is not allowed in 
releasing applications per NFPA 72. 

Cheers, 

Pat Thompson
NICET IV Special Hazards
ATS Alaska
Direct: 907-375-4176

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Duane Johnson
Sent: Friday, November 13, 2015 10:38 AM
To: [email protected]
Subject: RE: Cross zoned preaction detection

Cross zoned works, but personally I like double interlocked over cross zoned 
single interlock when you are discussing mitigation of damage.

Cross zoned will not help 'detect' a wider range of fires, it helps 'reduce' 
the amount of false activations. The more fire signatures you require (ie. 
Heat, smoke, IR, etc) prior to activation, the less false activations you will 
have. For example, a welders torch will activate both a heat detector and 
sprinkler (seen it), but not likely a photoelectric smoke detector and a 
sprinkler. So you add smoke detection as a way to mitigate non-fire heat 
sources from tripping the system. There is a good range of smoke detector types 
(ie photo, ionization, air sampling, etc) and fire alarm program adjustments 
(ie. Alarm verification, dirty, etc.) that can help reduce false activations.

One type of detection that seems good, at least on paper, is video detection. 
But I can't confirm field success. 

Duane Johnson, PE
Design Manager
Strickland Fire Protection
5113 Berwyn Road
College Park, MD 20740
301-474-1136 Office
301-455-0010 Cell


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Friday, November 13, 2015 12:37 PM
To: [email protected]
Subject: Cross zoned preaction detection

Does anyone have any strongly held opinions about cross-zoning of detectors for 
single-interlock preaction systems?  I haven't done one, and have usually 
fallen back on double-interlock when there is a heightened concern about 
accidental activation (earthquakes and all that).    My understanding is that 
when two different types of detectors are cross-zoned, it can help to detect a 
wider range of fires that may grow out of the incipient stages at different 
speed and/or with different release characteristics.   And cross-zoning with 
the same type of detector can give a heightened level of fail safety, so that 
seems more comparable to double-interlock.    I'm interested in hearing any 
suggestions, opinions of the value of this design (or not) and good or best 
practices.

Steve Leyton

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to