Those last two posts from Pat and Duane were great!  Good job guys, that is so 
helpful.

Scott

Office: (763) 425-1001 x 202
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Duane Johnson
Sent: Friday, November 13, 2015 7:29 PM
To: [email protected]
Subject: Re: Cross zoned preaction detection

No problem Pat, good post. 

To sum things up, IT DEPENDS. For example, had one client that wanted a double 
interlock for a 200 sq ft server room.  Just couldn't justify the added cost 
for two sprinklers. 

Other items that play a role in the decision tree are items such as area of 
protection, occupancy, ambient temperature, temperature fluctuations, ceiling 
arrangement, mission continuity, performance goals/objectives, etc. 

Special hazards opens up so many more things to discuss. 

Duane Johnson
Strickland Fire Protection
Sent from my iPhone

> On Nov 13, 2015, at 7:02 PM, Pat Thompson <[email protected]> wrote:
> 
> I agree on the whole with Duane, but for a couple of clarifications to his 
> statements that I'll hit on later. With over 40 years in the industry and 20 
> years in special hazards here's my take: it is true, using different 
> detection technologies and cross zoning them gives better assurance against 
> false or unwanted activations. In most cases it is also true that this kind 
> of setup will delay the activation of the valve. My question would be - is 
> this critical, given that the water is not going to deploy until a head fuses?
> 
> Modern technology in detection and control systems provides a range of 
> choices, I'll attempt to hit some highlights without getting long winded.  
> 
> In a setting where critical operations or artifacts are at risk we should as 
> an industry do what we can to ensure suppression is employed only when 
> needed, so double up on automatic detection via cross zone and even multiple 
> technologies. Or, as Duane suggests use double interlock.
> 
> On the other hand, if protecting a generator enclosure an accidental dowsing 
> of water is probably not going to be catastrophic; here single interlock on a 
> single detector activation rather than cross zone works just fine. My 
> practice has been to use heat detection in this setting and preferably flame 
> detection as well. Sometimes these are cross zoned, sometimes not. Speaking 
> to Steve's comment about incipient fires and their rate of growth, Class B 
> fuels do not take long to woosh into fully involved; flame detection will 
> give the quickest reaction for these fuels. 
> 
> Some will point out that flame detectors have caused them misery and pain due 
> to false activations. The industry and technologies have come a long way from 
> the first UV detectors (which caused me misery and pain back when) to the 
> point that when properly applied they are very reliable.
> 
> I would also mention that for automatic smoke or heat detection used for 
> suppression one should always reduce listed detector spacing by at least 
> half, sometimes more depending on conditions.
> 
> Bottom line is that application of detection is application specific. Air 
> sampling smoke detection is a great solution and provides lots of flexibility 
> in design and implementation - I love it. Spot smoke detection works well but 
> has challenges in high airflow or dirty environments. Heat detection is 
> reliable but generally slower to respond unless the fire has moved beyond the 
> incipient stage. 
> 
> As an aside, FMG's take on pre-action is to use heat detection and NOT cross 
> zone; whether single or double interlock. 
> 
> As this is a technical forum I want to point out a couple misstatements in 
> Duane's info. Nothing personal Duane, just sharing info. Firstly, ionization 
> smoke detectors are no longer available from any of the system manufactures 
> (hazmat disposal issues). Second, alarm verification is not allowed in 
> releasing applications per NFPA 72. 
> 
> Cheers,
> 
> Pat Thompson
> NICET IV Special Hazards
> ATS Alaska
> Direct: 907-375-4176
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Duane Johnson
> Sent: Friday, November 13, 2015 10:38 AM
> To: [email protected]
> Subject: RE: Cross zoned preaction detection
> 
> Cross zoned works, but personally I like double interlocked over cross zoned 
> single interlock when you are discussing mitigation of damage.
> 
> Cross zoned will not help 'detect' a wider range of fires, it helps 'reduce' 
> the amount of false activations. The more fire signatures you require (ie. 
> Heat, smoke, IR, etc) prior to activation, the less false activations you 
> will have. For example, a welders torch will activate both a heat detector 
> and sprinkler (seen it), but not likely a photoelectric smoke detector and a 
> sprinkler. So you add smoke detection as a way to mitigate non-fire heat 
> sources from tripping the system. There is a good range of smoke detector 
> types (ie photo, ionization, air sampling, etc) and fire alarm program 
> adjustments (ie. Alarm verification, dirty, etc.) that can help reduce false 
> activations.
> 
> One type of detection that seems good, at least on paper, is video detection. 
> But I can't confirm field success. 
> 
> Duane Johnson, PE
> Design Manager
> Strickland Fire Protection
> 5113 Berwyn Road
> College Park, MD 20740
> 301-474-1136 Office
> 301-455-0010 Cell
> 
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Steve Leyton
> Sent: Friday, November 13, 2015 12:37 PM
> To: [email protected]
> Subject: Cross zoned preaction detection
> 
> Does anyone have any strongly held opinions about cross-zoning of detectors 
> for single-interlock preaction systems?  I haven't done one, and have usually 
> fallen back on double-interlock when there is a heightened concern about 
> accidental activation (earthquakes and all that).    My understanding is that 
> when two different types of detectors are cross-zoned, it can help to detect 
> a wider range of fires that may grow out of the incipient stages at different 
> speed and/or with different release characteristics.   And cross-zoning with 
> the same type of detector can give a heightened level of fail safety, so that 
> seems more comparable to double-interlock.    I'm interested in hearing any 
> suggestions, opinions of the value of this design (or not) and good or best 
> practices.
> 
> Steve Leyton
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to