No sidewalls in duct.  1st they are not listed for that and it's just not 
necessary.  Depending on the duct size FlexHead has a great product for 
inserting sprinklers in ductwork.  Use standard pendant style sprinklers.

Also be sure to ask what is the normal operating temperature of the airstream 
in the duct and if there is an upset condition temperature increase variance.  
Get the right temp sprinkler.

If there is a fire in the booth you can bet on it migrating into the ductwork 
so assume it's all one flow event.

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Welch, Bobby
Sent: Monday, November 23, 2015 11:19 AM
To: [email protected]
Subject: Spray Application using flammable or combustible materials

I am doing the sprinkler design for a few paint booths and with this being my 
first one I have a few questions; 1. Does the individual spray area include the 
pendent sprinklers in the ceiling of the paint booth and the sprinklers in the 
exhaust duct? Whit the requirement of extra hazard group two is there a way 
that Horizontal sidewall sprinkler can be used in exhaust stacks.

 

Bobby Welch

Managing Partner



1081 B State Route 28, Box 213

Milford, OH 45150

Ph: 513-413-4500

Fax: 877-788-5980

Email: [email protected] 
<mailto:[email protected]> 

Web: www.veteranfireprotection.com <http://www.veteranfireprotection.com/> 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to