2015 code removes this requirement.

----- Original Message -----
From: Jerry Van Kolken <[email protected]>
To: [email protected]
Sent: Mon, 28 Sep 2015 18:44:58 -0400 (EDT)
Subject: Class 1 Standpipe Roof Valve

According to the NFPA 14-A.7.3.2(5) (13Ed.) There is gate valve installed
isolating the hose valve on the roof.  Is there verbiage about this
isolation valve? Is the valve required if you're not in areas subject to
freezing? 

 