You can tell them they need a 20" line and that they might want to have the
architect verify your findings.
.


On Tue, Dec 22, 2015 at 12:17 PM, Brian Harris <[email protected]>
wrote:

> Ron-
> I totally agree. We've ran into a couple instances where the civil site
> utility plan shows the underground size but then has a note that the fire
> sprinkler contractor has to verify it will work. I've been telling the GC
> the civil engineer is responsible for it but they keep pointing to the note
> on the plans that says we have to verify it will work. I tell them I'll
> verify it'll work for the sire sprinkler system but that's it, I'm not on
> the hook for anything else that is supplied by the same underground.
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Ron Fletcher
> Sent: Tuesday, December 22, 2015 2:14 PM
> To: [email protected]
> Subject: Re: Fire Flow vs Hydraulic calc's
>
> It's in Appendix B of IFC and is definitely in the realm of A/E team. Fire
> flow, hydrant spacing etc.. Is required for building permits (usually) and
> the fire line size should have been determined well before a sprinkler
> contractor was involved.
>
> Sent from my iPhone
>
> > On Dec 22, 2015, at 1:46 PM, Brian Harris <[email protected]>
> wrote:
> >
> > Can someone please put into laymen's terms the difference between doing
> a fire flow demand calc for the underground and the hydraulic calc's for
> the sprinkler system? We have been running into some projects lately where
> the civil engineer tries to pawn sizing the underground off onto the
> sprinkler contractor. I try telling them that's their responsibility not
> ours but I'd like something more definitive to have on hand.
> >
> > Brian Harris, CET
> > BVS Systems Inc.
> > Sprinkler Division
> > bvssystemsinc.com<http://bvssystemsinc.com/>
> > Phone: 704.896.9989
> > Fax: 704.896.1935
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to