OK what used to be simple is now a swirling mass of questions...

If you have pockets with residential sprinklers that require sprinklers -
in this case deeper than 12" - so you are forced to use sidewalls in them
and there are ceiling fans in the center of the pocket so you cannot
maintain the required 8'-0 minimum distance from the sidewall to fan....

So in a room that is 12'-0 x 14' -0 we either have 3 heads - if we assume
the sidewall in the soffit is sufficient for the intent of the code without
regard to the obstruction as the pendents on the perimeter will cover under
the fan...or 4 if that is not the case.

Has the committee discussed these situations?