Which standard? 13D you have to be at least 5 ft away from the fan motor for a HSW sprinkler and the pocket can be deeper than 12" as long as your under 100 cu. ft.
On Tue, Jan 12, 2016 at 6:29 AM, Greg McGahan <[email protected]> wrote: > OK what used to be simple is now a swirling mass of questions... > > If you have pockets with residential sprinklers that require sprinklers - > in this case deeper than 12" - so you are forced to use sidewalls in them > and there are ceiling fans in the center of the pocket so you cannot > maintain the required 8'-0 minimum distance from the sidewall to fan.... > > So in a room that is 12'-0 x 14' -0 we either have 3 heads - if we assume > the sidewall in the soffit is sufficient for the intent of the code without > regard to the obstruction as the pendents on the perimeter will cover under > the fan...or 4 if that is not the case. > > Has the committee discussed these situations? > > Thanks, > > > Greg McGahan > Living Water Fire Protection, LLC <http://www.livingwaterfp.com> > 1160 McKenzie Road > Cantonment, FL 32533 > 850-937-1850 > fax 850-937-1852 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org