Which standard? 13D you have to be at least 5 ft away from the fan motor
for a HSW sprinkler and the pocket can be deeper than 12" as long as your
under 100 cu. ft.

On Tue, Jan 12, 2016 at 6:29 AM, Greg McGahan <[email protected]> wrote:

> OK what used to be simple is now a swirling mass of questions...
>
> If you have pockets with residential sprinklers that require sprinklers -
> in this case deeper than 12" - so you are forced to use sidewalls in them
> and there are ceiling fans in the center of the pocket so you cannot
> maintain the required 8'-0 minimum distance from the sidewall to fan....
>
> So in a room that is 12'-0 x 14' -0 we either have 3 heads - if we assume
> the sidewall in the soffit is sufficient for the intent of the code without
> regard to the obstruction as the pendents on the perimeter will cover under
> the fan...or 4 if that is not the case.
>
> Has the committee discussed these situations?
>