I wouldn't jump the gun on the older systems. They were more than likely
pipe scheduled and don't require someone out there charging the owner a few
grand surveying and running new calcs on something that was never
hydraulically calculated in the first place. A visual inspection and the
age of the system should help determine that if all other information is
lacking.


On Mon, Feb 1, 2016 at 5:52 PM, rongreenman . <[email protected]> wrote:

> NFPA says to see that it conforms with 13 and 25. that would be format, not
> data. If it's not there it is a deficiency and needs to be replaced.
> (NFPA25/14 Table 5.5.1) Replacement may require a survey and re-calc but
> that is outside the scope of 25 and that is explicitly stated in the
> document. (NFPA25/14 5.5.3)
>
> On Mon, Feb 1, 2016 at 4:41 PM, Steve Leyton <[email protected]>
> wrote:
>
> > We have AHJ'S that will issue,a correction notice for missing placards.
> If
> > it is noted on an inspection as a deficiency, and if you're AHJs want
> > copies of inspections to be filed with them, then that would be a
> > potential  enforcement benchmark.
> >
> >
> > Steve
> >
> >
> > -------- Original message --------
> > From: [email protected]
> > Date: 2/1/2016 2:03 PM (GMT-07:00)
> > To: sprinklerforum <[email protected]>
> > Subject: Hydraulic Placards
> >
> > A client of mine has posed a question.
> > I understand part of a system inspection is to verify the adequacy of the
> > water supply. Many older buildings are missing the hydraulic placard on
> the
> > riser, and original plans/calcs are not available.
> >
> > A full-blown survey and hydraulic calculation is too expensive and the
> > owner will balk at it.
> >
> > Those of you who are involved in inspections, how do you handle this and
> > what would you recommend?
> > Would a rough 'guestimate' suffice depending on the occupancy?
> >
> >
> > Thank  you.
> >
> >
> >
> > Bill Menster
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to