Just got back to my desk. Look at section 8.3.3.3 (2013 edition) Mike Hill
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Michael Hill Sent: Thursday, February 18, 2016 2:15 PM To: [email protected] Subject: RE: Sprinkler Temp Vs. Response type Do not have NFPA 13 in front of me, but there is a section that allows you to use SR heads if there are no QR heads in the temperature that you need. Mike Hill -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Van Kolken Sent: Thursday, February 18, 2016 2:12 PM To: [email protected] Subject: Sprinkler Temp Vs. Response type I have a situation where there is a parts steam cleaner that will put out 250 deg. Steam when opened to remove parts. The sprinklers in the area are quick response type. I want to put Extra High temp heads (325 deg) over the cleaner, but I can only find them in standard response at that temp. Am I being over cautious with that high temp of rating? And would all the heads in the area have to be changed to standard response type? Jerry Van Kolken Millennium Fire Protection Corp. 2950 San Luis Rey Rd. Oceanside, CA 92058 (760) 722-2722 FX 722-2730 We Have Moved Please update your records with the new address _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org