Jerry

I'd also have a concern about corrosion. It sounds reasonable that warm moist 
air condensing on the heads would cause them to wet throughout the day.

Best


> On Feb 18, 2016, at 11:15, Michael Hill <[email protected]> wrote:
> 
> Do not have NFPA 13 in front of me, but there is a section that allows you
> to use SR heads if there are no QR heads in the temperature that you need.
> 
> Mike Hill
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Jerry Van Kolken
> Sent: Thursday, February 18, 2016 2:12 PM
> To: [email protected]
> Subject: Sprinkler Temp Vs. Response type
> 
> I have a situation where there is a parts steam cleaner that will put out
> 250 deg. Steam when opened to remove parts. The sprinklers in the area are
> quick response type.  I want to put Extra High temp heads (325 deg) over the
> cleaner, but I can only find them in standard response at that temp. Am I
> being over cautious with that high temp of rating? And would all the heads
> in the area have to be changed to standard response type?
> 
> 
> 
> Jerry Van Kolken
> 
> Millennium Fire Protection Corp.
> 
> 2950 San Luis Rey Rd.
> 
> Oceanside, CA 92058
> 
> (760) 722-2722 FX 722-2730
> 
> 
> 
> We Have Moved Please update your records with the new address
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to