On Thu, Feb 18, 2016 at 4:47 PM, Travis Mack, SET <[email protected]>
wrote:

> I have seen mains routed over the roof in several instances.  Some were
> industrial, some were freezer storage buildings.  We just always had
> structural engineer verify everything.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 2/18/2016 5:46 PM, Ed Vining wrote:
>
>> Frans, in the 1970's or 80's an unprotected fire protection main was
>> installed on the roof of the C&H Sugar Company at Crockett California. I
>> don't remember the size, but believe it was at least eight inch.  The
>> lowest temperature I can find at that location is 28 degrees F.  As far as
>> I know the pipe has never frozen. You could question them at:
>>
>>     -
>> *830 Loring Ave​,  Crockett, CA 94525*
>>     -  Phone number (510) 787-2121
>>
>>
>>
>> On Thu, Feb 18, 2016 at 3:45 PM, Frans Stoop <[email protected]> wrote:
>>
>> Dear colleagues,
>>>
>>> A client has an existing alarm valve room in an open air courtyard of his
>>> complex building, fully enclosed by parts of the building.
>>> It may freeze in this coutry, sometimes upto -20 deg C (-4 deg F).
>>> We are looking for a way to connect the valve room to the underground
>>> fire
>>> water mains outside the perimeter of the building by way of a new DN300
>>> (12
>>> inch) header.
>>> Passing through the building or its souterrain is very difficult or might
>>> even be impossible.
>>> (All rooms, including the souterrain are in full use and have access
>>> limitations.)
>>> Drilling a tunnel underneath the souterrain has been rejected because of
>>> possible damage to the foundation and all the existing pipes and cables
>>> that might lay under the building.
>>>
>>> Client has come up with a proposal to route this 12 inch header over the
>>> roof, meaning 14 m up along the outside wall, 17 m horizontal over the
>>> roof
>>> and 14 m down again into the courtyard.
>>> That above ground loop would be made in hot-dipped galvanized steel,
>>> insulated and heat-traced.
>>>
>>> What is your opinion about that solution?
>>> And why?
>>> Has this been done often?
>>> Looking forward to your appreciated views.
>>>
>>> Met vriendelijke groet/Kind regards,
>>>
>>> Frans Stoop
>>> Riskonet B.V.
>>> Singel 540, 1017AZ, Amsterdam
>>> T +31 6542 37 642
>>> www.riskonet.com
>>> [email protected]
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>>
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
Cell 925-787-0465
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to