Hello,
I have a flammable liquid storage room , with an area of less than 500 square feet, that will be used for the storage and dispensing of Class IB, IC, II, and IIIA liquids in drums on racks. The drums will be on side, with two storage levels to a height of roughly 6 ft. Some of the drums will be plastic. In trying to determine the protection criteria from NFPA 30, I keep ending up at Table 16.5.2.7, which requires a ceiling density of 0.45/entire area, plus horizontal barriers, plus 2 levels of in-racks. This appears excessive. Are there any other options? I seem to recall that we could protect a liquid storage room (having an area of less than 500 sq. ft.) with a density of 0.60/entire room, regardless of the type of drums. David Bitton, ing. Les services de prévention des sinistres Quest inc. Quest Loss Control Services Inc. 5100, rue de la Savane, bureau 200 Montréal, QC H4P 1T8 (514) 341-4545 www.questlosscontrol.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org