Thank you Craig for your response.  I don't have a problem with the 0.45 or
even 0.60 density.  My issue is with the horizontal barriers and in-rack
sprinklers. The decision tree sends me to Table 16.5.2.7, which is
applicable for storage up to 25 ft. In this room, drums will be stored on
side to a height of 6 ft. The room will be used for dispensing from drums to
smaller containers.  There won't be any empty plastic drums. I looked at FM
Data Sheet 7-29 and their protection criteria are also set up for storage to
25 or 30 ft.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Monday, February 29, 2016 8:43 AM
To: [email protected]
Subject: RE: Liquid Storage Room

That table is for water miscible liquids.  So you better be sure that ALL of
the liquids stored are water miscible.  I'd be surprised if that was the
case.  

Have you worked through the applicable decision tree, probably 16.4.1(b)?

Plastics will generate worst case but if the Class IB is in metal you also
need to reconcile that hazard then design to the worst case.  

A 0.45 or even a 0.60 gpm/sf density for some materials is not unusual
especially when dealing with non-miscibles.  Even with miscible liquids the
amount of water needed to dilute it to a point where it can be considered a
lesser hazard can be extremely high.   

I'd also ask if they plan to store empty plastic drums in this area as that
can add another factor to the mix.  

If you just hit a brick wall I'd suggest looking to the FM Global Data
sheets for additional guidance in dealing with flammable/combustible storage
protection criteria.


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of David Bitton
Sent: Friday, February 26, 2016 12:32 PM
To: [email protected]
Subject: Liquid Storage Room

Hello,

 

I have a flammable liquid storage room , with an area of less than 500
square feet, that  will be used for the storage and dispensing of Class IB,
IC, II, and IIIA liquids in drums on racks.  The drums will be on side, with
two storage levels to a height of roughly 6 ft.  Some of the drums will be
plastic.  In trying to determine the protection criteria from NFPA 30, I
keep ending up at Table 16.5.2.7, which requires a ceiling density of
0.45/entire area, plus horizontal barriers, plus 2 levels of in-racks.  This
appears excessive.  Are there any other options? 

 

I seem to recall that we could protect a liquid storage room (having an area
of less than 500 sq. ft.) with a density of 0.60/entire room, regardless of
the type of drums.

 

David Bitton, ing.

Les services de prévention des sinistres Quest inc.

Quest Loss Control Services Inc.

5100, rue de la Savane, bureau 200

Montréal, QC H4P 1T8

(514) 341-4545

www.questlosscontrol.com

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to