Thank you Craig for your response. I don't have a problem with the 0.45 or even 0.60 density. My issue is with the horizontal barriers and in-rack sprinklers. The decision tree sends me to Table 16.5.2.7, which is applicable for storage up to 25 ft. In this room, drums will be stored on side to a height of 6 ft. The room will be used for dispensing from drums to smaller containers. There won't be any empty plastic drums. I looked at FM Data Sheet 7-29 and their protection criteria are also set up for storage to 25 or 30 ft.
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Monday, February 29, 2016 8:43 AM To: [email protected] Subject: RE: Liquid Storage Room That table is for water miscible liquids. So you better be sure that ALL of the liquids stored are water miscible. I'd be surprised if that was the case. Have you worked through the applicable decision tree, probably 16.4.1(b)? Plastics will generate worst case but if the Class IB is in metal you also need to reconcile that hazard then design to the worst case. A 0.45 or even a 0.60 gpm/sf density for some materials is not unusual especially when dealing with non-miscibles. Even with miscible liquids the amount of water needed to dilute it to a point where it can be considered a lesser hazard can be extremely high. I'd also ask if they plan to store empty plastic drums in this area as that can add another factor to the mix. If you just hit a brick wall I'd suggest looking to the FM Global Data sheets for additional guidance in dealing with flammable/combustible storage protection criteria. Craig L. Prahl Fire Protection Group Lead/SME CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29303 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of David Bitton Sent: Friday, February 26, 2016 12:32 PM To: [email protected] Subject: Liquid Storage Room Hello, I have a flammable liquid storage room , with an area of less than 500 square feet, that will be used for the storage and dispensing of Class IB, IC, II, and IIIA liquids in drums on racks. The drums will be on side, with two storage levels to a height of roughly 6 ft. Some of the drums will be plastic. In trying to determine the protection criteria from NFPA 30, I keep ending up at Table 16.5.2.7, which requires a ceiling density of 0.45/entire area, plus horizontal barriers, plus 2 levels of in-racks. This appears excessive. Are there any other options? I seem to recall that we could protect a liquid storage room (having an area of less than 500 sq. ft.) with a density of 0.60/entire room, regardless of the type of drums. David Bitton, ing. Les services de prévention des sinistres Quest inc. Quest Loss Control Services Inc. 5100, rue de la Savane, bureau 200 Montréal, QC H4P 1T8 (514) 341-4545 www.questlosscontrol.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org