Unless it is a pre-planned fire, you may not be able to get everyone out of the pool before the fire pump kicks in. You don't always get a lot of lead time.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2] On Mon, Mar 7, 2016 at 11:40 AM, [email protected] <[email protected]>
wrote:
Um, if there's a fire and the pool was being used as a suction source, I'd think
they would require everyone out of the pool?

It is not uncommon to use swimming pools as a fire water source in lieu of a
storage tank. Also decorative fountain ponds, cooling tower basins, etc.

Craig L. Prahl
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC 29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Todd Williams
Sent: Monday, March 07, 2016 11:35 AM
To: [email protected]
Subject: Re: Pool as Firewater Source

You might have a health code issue with that. How could you prevent someone from getting stuck in a suction line? There are strict requirements as far as pool recirculating drains and I am not sure you could meet those with a fire pump suction line. That could create a huge liability problem. I was asked to look at
one of these a few years back and I suggested they call my competition.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Mon, Mar 7, 2016 at 11:27 AM, Richard Mote <[email protected]>
wrote:
Other than the fact that I don't think it's a good idea. Is there anything an any code that prohibits the use of a heated swimming pool as a fire pump source.
We've actually done one using an indoor pool at a hotel. This would be an
outdoor pool, using geo-thermal heating.

Richard L. Mote CET

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to