My only experience was a rural mint oil facility near Yakima, WA.  They used 
the community pool as the fire water source (or used the need for fire water as 
a reason to install community pool).

I know that there are safeguards that MUST be put in place to prevent the 
potential of a swimmer being stuck against an intake - others have touched on 
some of those - but it is a real problem and there are documented cases of 
people being hurt in that manner (see Steve's post).

Remember also that we need to protect against injury during annual testing, 
where the contractor may not be aware of the water source or the presence - or 
lack thereof - of such safeguards.

As  side note - the mint oil facility has a major water demand that would 
easily lead to harm of swimmers if precautions were not taken.  Hopefully, this 
light hazard/residential facility has small enough demands to make safeguards 
that much easier.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Monday, March 7, 2016 11:22 AM
To: [email protected]
Subject: Re: Pool as Firewater Source

So a residential facility? Or at worst light hazard? So you wouldn't have a 
huge GPM demand in either case. Or does12,000 gal translate to 120gpm for an 
hour? What I'm thinking is that a weir and a large supply side pipe could 
mitigate against a fast suction in the pool. Then pre-fill the system with 
fresh water if the treated water from the pool is a consideration for the 
piping. Shut down power to pool pumps when the fire pump kicks in. This does 
not sound like an unsolvable problem and I've seen high rise hotel pools of 
upper floors used as secondary fire water.

On Mon, Mar 7, 2016 at 9:08 AM, Richard Mote <[email protected]>
wrote:

> This project is an existing building (church) in the middle of nowhere
> being converted to a drug and alcohol rehabilitation facility. Since
> there is now going to be people living in the building, the AHJ is
> requiring the facility be sprinklered. We have quoted both an
> underground  tank and above ground tank for the water supply. We only
> need around 12,000 gallons for a water supply. The owner now is coming
> back and saying "for the price of either tank arrangement I can put in
> a therapy pool". The last one we did had signs all around the pool,
> that when the alarm sounded they were to exit the pool immediately. We
> would also make it clear in our proposal that if they convert to salt water 
> all warrantees are void.
>
> Richard L. Mote CET
> Rowe Sprinkler Systems, Inc.
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Joe
> Sent: Monday, March 07, 2016 11:54 AM
> To: [email protected]
> Subject: Re: Pool as Firewater Source
>
> Just something for an owner to think about: I saw one of these in a
> huge resort in the middle of nowhere. All of the sprinkler lines had
> issues in all of the buildings.
>
> Over time, the management and the engineering staff had changed
> loosing knowledge of the systems. The chlorine pool became a salt
> water pool and this cycle changed a few times. All of this did appear
> to add to the sprinkler line issues.
>
> Replacement of all the sprinkler lines in a finished was a bit costly.
>
>
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to