The IMC says to sprinkler 10-inch diameter and larger ducts where 
combustibles are handled.

John F. Hoffman, PE*  \  Burns & McDonnell
Senior Fire Protection Engineer
O 816-349-6759 \  M 816-255-4102 
[email protected]  \  burnsmcd.com
9400 Ward Parkway  \  Kansas City, MO 64114

Proud to be one of FORTUNE's 100 Best Companies to Work For
Please consider the environment before printing this email.
*Registered in: MO

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Todd Williams
Sent: Tuesday, March 15, 2016 10:41 AM
To: [email protected]
Subject: Minimum duct size for sprinklers

I am working with a facility that makes envelopes and other office paper 
products. They have an exhaust duct system which feeds twin collectors outside.
The collectors have built in sprinklers and 1" outlets to connect to. The owner 
wants to connect to the sprinklers in the collector, but a contractor told them 
they should sprinkler all of the ductwork as well. The largest feed ducts are 
16" round, decrease down to 11" round and connect to the machines with smaller 
duct (all round). My question is what is the minimum size duct you should 
install a sprinkler in? NFPA 654 had no guidance.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to