NFPA 91 says 75in² or larger or just under 10" diameter

-----Original Message-----
From: Todd Williams [mailto:[email protected]] 
Sent: Tuesday, March 15, 2016 8:41 AM
To: [email protected]
Subject: Minimum duct size for sprinklers

I am working with a facility that makes envelopes and other office paper 
products. They have an exhaust duct system which feeds twin collectors outside.
The collectors have built in sprinklers and 1" outlets to connect to. The owner 
wants to connect to the sprinklers in the collector, but a contractor told them 
they should sprinkler all of the ductwork as well. The largest feed ducts are 
16" round, decrease down to 11" round and connect to the machines with smaller 
duct (all round). My question is what is the minimum size duct you should 
install a sprinkler in? NFPA 654 had no guidance.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)