Nope. Smoothness above the sprinkler only affects activation times, and the
differences are only a few seconds.
Do you worry if the intermediate framing members are 2x4, 2x6, 2x8, or 2x10
(a 6" variation)? Do you worry if they are perpendicular or  parallel to
the throw? No, because min deflector distance for back-to-back at the peak
is 16". This is to get the throw beneath the 'unsmoothness' of the bottom
of the deck.
The U.L. tests of Tyco BB heads 'started' with previously listed QR, EC
heads- only the Deflectors were changed, and the throw patterns at
different pressures were measured. They did that by not changing the bottom
of the deck or changing deflector distance, but by raising and lowering the
Floor :).

And actually I think a little roughness at the bottom of the deck might
even enhance activation a bit-- but I am certainly no Sprinkler Scientist-
and the Modeling of BB heads activation and patterns I have done has been
rather coarse, i.e., quick and dirty ;)

b
On Mar 29, 2016 9:46 AM, "Brian Harris" <[email protected]> wrote:

> I talked with tech support and while he wasn't too concerned about the
> roughness off the insulation he did agree the insulation needs to be
> "shaved" to a uniform depth to assure proper deflector distances.
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Bruce Verhei
> Sent: Tuesday, March 29, 2016 10:44 AM
> To: [email protected]
> Subject: Re: Tyco Attic Heads
>
> I like Matt's advice. Tyco may have information from original test series.
> Sometimes some of conditions are to meet extreme distance or a minimum
> available pressure.
>
> While I'd repeat that Tyco's comments would apply to this particular
> project only, could you post?
>
> Best
>
> Bruce
>
> > On Mar 29, 2016, at 06:41, Matt Grise <[email protected]> wrote:
> >
> > I would call tyco's technical hotline.
> >
> > Matt Grisé PE*, LEED AP, NICET II
> > Sales Engineer
> > Alliance Fire Protection
> > 130 w 9th Ave.
> > North Kansas City, MO 64116
> >
> > *Licensed in KS & MO
> >
> > 913.888.0647 ph
> > 913.888.0618 f
> > 913.526.7443 cell
> > www. AFPsprink.com
> >
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum
> > [mailto:[email protected]] On Behalf Of
> > Brian Harris
> > Sent: Tuesday, March 29, 2016 8:40 AM
> > To: [email protected]
> > Subject: RE: Tyco Attic Heads
> >
> > "bounce..."
> >
> > Brian Harris, CET
> > BVS Systems Inc.
> > bvssytemsinc.com
> >
> > -----Original Message-----
> > From: Sprinklerforum
> > [mailto:[email protected]] On Behalf Of
> > Brian Harris
> > Sent: Tuesday, March 29, 2016 8:23 AM
> > To: [email protected]
> > Subject: Tyco Attic Heads
> >
> > Working on a project that we've installed Tyco attic heads and the GC
> has now gone in and added roughly several inches of spray on insulation.
> When I say roughly I mean roughly, the depth varies from 6" to 12" with no
> consistency what so ever. I've told them that most of the piping will have
> to be lowered to stay within the required clearances but I also think the
> insulation needs to be "shaved" to a smooth consistent finish, obviously
> that didn't go over so well. Since attic heads are considered extended
> coverage I think it's safe to assume they need to be installed per the
> requirements of NFPA as well, under a smooth flat surface. Am I missing
> something?
> >
> > Brian Harris, CET
> > BVS Systems Inc.
> > Sprinkler Division
> > bvssystemsinc.com<http://bvssystemsinc.com/>
> > Phone: 704.896.9989
> > Fax: 704.896.1935
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to