Brian:

Your problem has been very clear from the beginning. 

My guess is you would have to drop the main to about 2' below the lowest point 
of insulation. Then field cut every sprig. Couple that with a sloping dry 
system and you have an installation nightmare. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Mar 29, 2016, at 12:58 PM, Brian Harris <[email protected]> wrote:
> 
> Brad-
> You're missing the point or maybe I haven't explained it clearly which is 
> entirely probable. The deflector distance is no longer taken from the roof 
> deck, it has to be taken from the bottom of the insulation. With the 
> insulation varying greatly in thickness it is damn near impossible to install 
> the system with some reasonable sense of order. Hence the reason for "some 
> kind of iso-surface".
> 
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Brad Casterline
> Sent: Tuesday, March 29, 2016 1:50 PM
> To: [email protected]
> Subject: RE: Tyco Attic Heads
> 
> In other words, only where the intermediate members exceed 10" depth, will it 
> Maybe need a shave - a few inches deep by six feet long.
> It is ludicrous to insist on some kind of insulation iso-surface for things 
> to work right!
>> On Mar 29, 2016 12:28 PM, "Brad Casterline" <[email protected]> wrote:
>> 
>> 
>> It would only be a problem if the rafter depth plus gob depth exceeded 
>> deflector depth, so you're looking at 16" to 22" (6" variation, like 
>> you said).
>> 
>> But in that regard, it is not an activation issue, it is only an 
>> obstruction issue.
>> Shave it where necessary to not be an obstruction?
>> On Mar 29, 2016 12:07 PM, "Brian Harris" <[email protected]>
>> wrote:
>> 
>>> Brad-
>>> The real issue we're having is the haphazard way the sprayed on 
>>> insulation was installed, there's no way to establish minimum & 
>>> maximum deflector distances.
>>> 
>>> Brian Harris, CET
>>> BVS Systems Inc.
>>> bvssytemsinc.com
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum [mailto:
>>> [email protected]] On Behalf Of Brad 
>>> Casterline
>>> Sent: Tuesday, March 29, 2016 11:23 AM
>>> To: [email protected]
>>> Subject: RE: Tyco Attic Heads
>>> 
>>> Nope. Smoothness above the sprinkler only affects activation times, 
>>> and the differences are only a few seconds.
>>> Do you worry if the intermediate framing members are 2x4, 2x6, 2x8, 
>>> or
>>> 2x10 (a 6" variation)? Do you worry if they are perpendicular or  
>>> parallel to the throw? No, because min deflector distance for 
>>> back-to-back at the peak is 16". This is to get the throw beneath the 
>>> 'unsmoothness' of the bottom of the deck.
>>> The U.L. tests of Tyco BB heads 'started' with previously listed QR, 
>>> EC
>>> heads- only the Deflectors were changed, and the throw patterns at 
>>> different pressures were measured. They did that by not changing the 
>>> bottom of the deck or changing deflector distance, but by raising and 
>>> lowering the Floor :).
>>> 
>>> And actually I think a little roughness at the bottom of the deck 
>>> might even enhance activation a bit-- but I am certainly no Sprinkler 
>>> Scientist- and the Modeling of BB heads activation and patterns I 
>>> have done has been rather coarse, i.e., quick and dirty ;)
>>> 
>>> b
>>> On Mar 29, 2016 9:46 AM, "Brian Harris" <[email protected]>
>>> wrote:
>>> 
>>>> I talked with tech support and while he wasn't too concerned about 
>>>> the roughness off the insulation he did agree the insulation needs 
>>>> to be "shaved" to a uniform depth to assure proper deflector distances.
>>>> 
>>>> Brian Harris, CET
>>>> BVS Systems Inc.
>>>> bvssytemsinc.com
>>>> 
>>>> 
>>>> -----Original Message-----
>>>> From: Sprinklerforum [mailto:
>>>> [email protected]] On Behalf Of Bruce 
>>>> Verhei
>>>> Sent: Tuesday, March 29, 2016 10:44 AM
>>>> To: [email protected]
>>>> Subject: Re: Tyco Attic Heads
>>>> 
>>>> I like Matt's advice. Tyco may have information from original test
>>> series.
>>>> Sometimes some of conditions are to meet extreme distance or a 
>>>> minimum available pressure.
>>>> 
>>>> While I'd repeat that Tyco's comments would apply to this 
>>>> particular project only, could you post?
>>>> 
>>>> Best
>>>> 
>>>> Bruce
>>>> 
>>>>> On Mar 29, 2016, at 06:41, Matt Grise <[email protected]> wrote:
>>>>> 
>>>>> I would call tyco's technical hotline.
>>>>> 
>>>>> Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire 
>>>>> Protection
>>>>> 130 w 9th Ave.
>>>>> North Kansas City, MO 64116
>>>>> 
>>>>> *Licensed in KS & MO
>>>>> 
>>>>> 913.888.0647 ph
>>>>> 913.888.0618 f
>>>>> 913.526.7443 cell
>>>>> www. AFPsprink.com
>>>>> 
>>>>> 
>>>>> 
>>>>> -----Original Message-----
>>>>> From: Sprinklerforum
>>>>> [mailto:[email protected]] On Behalf 
>>>>> Of Brian Harris
>>>>> Sent: Tuesday, March 29, 2016 8:40 AM
>>>>> To: [email protected]
>>>>> Subject: RE: Tyco Attic Heads
>>>>> 
>>>>> "bounce..."
>>>>> 
>>>>> Brian Harris, CET
>>>>> BVS Systems Inc.
>>>>> bvssytemsinc.com
>>>>> 
>>>>> -----Original Message-----
>>>>> From: Sprinklerforum
>>>>> [mailto:[email protected]] On Behalf 
>>>>> Of Brian Harris
>>>>> Sent: Tuesday, March 29, 2016 8:23 AM
>>>>> To: [email protected]
>>>>> Subject: Tyco Attic Heads
>>>>> 
>>>>> Working on a project that we've installed Tyco attic heads and 
>>>>> the GC
>>>> has now gone in and added roughly several inches of spray on insulation.
>>>> When I say roughly I mean roughly, the depth varies from 6" to 12"
>>>> with no consistency what so ever. I've told them that most of the 
>>>> piping will have to be lowered to stay within the required 
>>>> clearances but I also think the insulation needs to be "shaved" to 
>>>> a smooth consistent finish, obviously that didn't go over so well. 
>>>> Since attic heads are considered extended coverage I think it's 
>>>> safe to assume they need to be installed per the requirements of 
>>>> NFPA as well, under a smooth flat surface. Am I missing something?
>>>>> 
>>>>> Brian Harris, CET
>>>>> BVS Systems Inc.
>>>>> Sprinkler Division
>>>>> bvssystemsinc.com<http://bvssystemsinc.com/>
>>>>> Phone: 704.896.9989
>>>>> Fax: 704.896.1935
>>>>> 
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
>>>>> rin kl er.org _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
>>>>> rin kl er.org _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
>>>>> rin
>>>>> kl
>>>>> er.org
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>> nkl er.org _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>> nkl
>>>> er.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> ler.org _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> ler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________