Matthew,

Without insulation the distances are 16 to 22. With insulation as Brian
said 6 to 12,  1 would be an apparition
;)
On Mar 29, 2016 10:20 PM, "Matthew J Willis" <[email protected]> wrote:

> This is not suitability. This is distance from the deck. Plain and simple.
> Sounds like there are distances of 1 to who knows. Good job all..
>
>
>
> Sent from my Verizon Wireless 4G LTE smartphone
>
>
> -------- Original message --------
> From: Russell & Carol Gregory <[email protected]>
> Date: 03/29/2016 8:29 PM (GMT-07:00)
> To: [email protected]
> Subject: RE: Tyco Attic Heads
>
> Brian,
> I see no reference to the flammability of this spray on insulation. If it
> is flammable then the whole question of suitability of sprinklers without
> covering the insulation would become the issue.
> Regards,
> Russell Gregory
> Christchurch
> New Zealand
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brian Harris
> Sent: Wednesday, 30 March 2016 9:37 AM
> To: [email protected]
> Subject: RE: Tyco Attic Heads
>
> Travis-
> Yup that about sums it up, I thought I was losing my mind there for a
> minute.....
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Travis Mack
> Sent: Tuesday, March 29, 2016 4:05 PM
> To: [email protected]
> Subject: Re: Tyco Attic Heads
>
> Brian:
>
> Your problem has been very clear from the beginning.
>
> My guess is you would have to drop the main to about 2' below the lowest
> point of insulation. Then field cut every sprig. Couple that with a sloping
> dry system and you have an installation nightmare.
>
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook:
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>
> Sent from my iPhone
>
> > On Mar 29, 2016, at 12:58 PM, Brian Harris <[email protected]>
> wrote:
> >
> > Brad-
> > You're missing the point or maybe I haven't explained it clearly which
> is entirely probable. The deflector distance is no longer taken from the
> roof deck, it has to be taken from the bottom of the insulation. With the
> insulation varying greatly in thickness it is damn near impossible to
> install the system with some reasonable sense of order. Hence the reason
> for "some kind of iso-surface".
> >
> > Brian Harris, CET
> > BVS Systems Inc.
> > bvssytemsinc.com
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum
> > [mailto:[email protected]] On Behalf Of
> > Brad Casterline
> > Sent: Tuesday, March 29, 2016 1:50 PM
> > To: [email protected]
> > Subject: RE: Tyco Attic Heads
> >
> > In other words, only where the intermediate members exceed 10" depth,
> will it Maybe need a shave - a few inches deep by six feet long.
> > It is ludicrous to insist on some kind of insulation iso-surface for
> things to work right!
> >> On Mar 29, 2016 12:28 PM, "Brad Casterline" <[email protected]>
> wrote:
> >>
> >>
> >> It would only be a problem if the rafter depth plus gob depth
> >> exceeded deflector depth, so you're looking at 16" to 22" (6"
> >> variation, like you said).
> >>
> >> But in that regard, it is not an activation issue, it is only an
> >> obstruction issue.
> >> Shave it where necessary to not be an obstruction?
> >> On Mar 29, 2016 12:07 PM, "Brian Harris" <[email protected]>
> >> wrote:
> >>
> >>> Brad-
> >>> The real issue we're having is the haphazard way the sprayed on
> >>> insulation was installed, there's no way to establish minimum &
> >>> maximum deflector distances.
> >>>
> >>> Brian Harris, CET
> >>> BVS Systems Inc.
> >>> bvssytemsinc.com
> >>>
> >>>
> >>> -----Original Message-----
> >>> From: Sprinklerforum [mailto:
> >>> [email protected]] On Behalf Of Brad
> >>> Casterline
> >>> Sent: Tuesday, March 29, 2016 11:23 AM
> >>> To: [email protected]
> >>> Subject: RE: Tyco Attic Heads
> >>>
> >>> Nope. Smoothness above the sprinkler only affects activation times,
> >>> and the differences are only a few seconds.
> >>> Do you worry if the intermediate framing members are 2x4, 2x6, 2x8,
> >>> or
> >>> 2x10 (a 6" variation)? Do you worry if they are perpendicular or
> >>> parallel to the throw? No, because min deflector distance for
> >>> back-to-back at the peak is 16". This is to get the throw beneath
> >>> the 'unsmoothness' of the bottom of the deck.
> >>> The U.L. tests of Tyco BB heads 'started' with previously listed QR,
> >>> EC
> >>> heads- only the Deflectors were changed, and the throw patterns at
> >>> different pressures were measured. They did that by not changing the
> >>> bottom of the deck or changing deflector distance, but by raising
> >>> and lowering the Floor :).
> >>>
> >>> And actually I think a little roughness at the bottom of the deck
> >>> might even enhance activation a bit-- but I am certainly no
> >>> Sprinkler
> >>> Scientist- and the Modeling of BB heads activation and patterns I
> >>> have done has been rather coarse, i.e., quick and dirty ;)
> >>>
> >>> b
> >>> On Mar 29, 2016 9:46 AM, "Brian Harris" <[email protected]>
> >>> wrote:
> >>>
> >>>> I talked with tech support and while he wasn't too concerned about
> >>>> the roughness off the insulation he did agree the insulation needs
> >>>> to be "shaved" to a uniform depth to assure proper deflector
> distances.
> >>>>
> >>>> Brian Harris, CET
> >>>> BVS Systems Inc.
> >>>> bvssytemsinc.com
> >>>>
> >>>>
> >>>> -----Original Message-----
> >>>> From: Sprinklerforum [mailto:
> >>>> [email protected]] On Behalf Of Bruce
> >>>> Verhei
> >>>> Sent: Tuesday, March 29, 2016 10:44 AM
> >>>> To: [email protected]
> >>>> Subject: Re: Tyco Attic Heads
> >>>>
> >>>> I like Matt's advice. Tyco may have information from original test
> >>> series.
> >>>> Sometimes some of conditions are to meet extreme distance or a
> >>>> minimum available pressure.
> >>>>
> >>>> While I'd repeat that Tyco's comments would apply to this
> >>>> particular project only, could you post?
> >>>>
> >>>> Best
> >>>>
> >>>> Bruce
> >>>>
> >>>>> On Mar 29, 2016, at 06:41, Matt Grise <[email protected]> wrote:
> >>>>>
> >>>>> I would call tyco's technical hotline.
> >>>>>
> >>>>> Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire
> >>>>> Protection
> >>>>> 130 w 9th Ave.
> >>>>> North Kansas City, MO 64116
> >>>>>
> >>>>> *Licensed in KS & MO
> >>>>>
> >>>>> 913.888.0647 ph
> >>>>> 913.888.0618 f
> >>>>> 913.526.7443 cell
> >>>>> www. AFPsprink.com
> >>>>>
> >>>>>
> >>>>>
> >>>>> -----Original Message-----
> >>>>> From: Sprinklerforum
> >>>>> [mailto:[email protected]] On Behalf
> >>>>> Of Brian Harris
> >>>>> Sent: Tuesday, March 29, 2016 8:40 AM
> >>>>> To: [email protected]
> >>>>> Subject: RE: Tyco Attic Heads
> >>>>>
> >>>>> "bounce..."
> >>>>>
> >>>>> Brian Harris, CET
> >>>>> BVS Systems Inc.
> >>>>> bvssytemsinc.com
> >>>>>
> >>>>> -----Original Message-----
> >>>>> From: Sprinklerforum
> >>>>> [mailto:[email protected]] On Behalf
> >>>>> Of Brian Harris
> >>>>> Sent: Tuesday, March 29, 2016 8:23 AM
> >>>>> To: [email protected]
> >>>>> Subject: Tyco Attic Heads
> >>>>>
> >>>>> Working on a project that we've installed Tyco attic heads and the
> >>>>> GC
> >>>> has now gone in and added roughly several inches of spray on
> insulation.
> >>>> When I say roughly I mean roughly, the depth varies from 6" to 12"
> >>>> with no consistency what so ever. I've told them that most of the
> >>>> piping will have to be lowered to stay within the required
> >>>> clearances but I also think the insulation needs to be "shaved" to
> >>>> a smooth consistent finish, obviously that didn't go over so well.
> >>>> Since attic heads are considered extended coverage I think it's
> >>>> safe to assume they need to be installed per the requirements of
> >>>> NFPA as well, under a smooth flat surface. Am I missing something?
> >>>>>
> >>>>> Brian Harris, CET
> >>>>> BVS Systems Inc.
> >>>>> Sprinkler Division
> >>>>> bvssystemsinc.com<http://bvssystemsinc.com/>
> >>>>> Phone: 704.896.9989
> >>>>> Fax: 704.896.1935
> >>>>>
> >>>>> _______________________________________________
> >>>>> Sprinklerforum mailing list
> >>>>> [email protected]
> >>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
> >>>>> rin kl er.org _______________________________________________
> >>>>> Sprinklerforum mailing list
> >>>>> [email protected]
> >>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
> >>>>> rin kl er.org _______________________________________________
> >>>>> Sprinklerforum mailing list
> >>>>> [email protected]
> >>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
> >>>>> rin
> >>>>> kl
> >>>>> er.org
> >>>>
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>>
> >>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
> >>>> nkl er.org _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>>
> >>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
> >>>> nkl
> >>>> er.org
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> k ler.org _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> k
> >>> ler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________