I use the acceleration due to gravity for my conversions because I think it
would be the same in France (they invented the metric system) as it is in
England:
32.2 ft/sec/sec divided by 9.81 m/sec/sec = 3.???????? ft per meter.

Brad
On Apr 20, 2016 5:42 PM, "James Crawford" <[email protected]> wrote:

> NFPA #13 (2013) section 8.12.3.2 minimum distance between ESFR heads not
> less than 8’-0” or (2.4 m)
>
>
>
> We are looking at a project and the ESFR heads are space at 2.4 meters
> apart
> and this seems to meet code, but 2.4 m equals 7’-10 ½”.
>
>
>
> Is this an over site by NFPA or are you allowed to be less than 8’-0” or
> should it be 2.439 m and was just missed in the conversion.
>
>
>
> This would be the same for the obstruction rule 1’-0” is 0.305 m not 0.3 m
> and 2’-0” is 0.610 m not 0.60 m
>
>
>
> Just wondering.
>
>
>
>
>
> Thank you
>
>
>
>
>
> James Crawford
>
> Phaser Fire Protection Ltd.
>
> Phone  604-888-0318
>
> Fax 604-888-4732
>
> Cel 604-790-0938
>
> Email  [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to