James,
I believe you'll find your answer in section 1.6.1.4 (in the '13 and '16 editions) which reads:

   1.6.1.4 If a value for measurement as given in this standard is
   followed by an equivalent value in other units, the first stated
   shall be regarded as the  requirement.

Also, the '16 edition contains the following paragraph:

   1.6.3* Some dimensions used in this standard are exact and some are
   not. Nominal dimension are often used, such as the
   dimensions used for pipe sizes. The metric equivalent shown in this
   standard might not be an exact conversion to the SI unit, but the
   nominal metric equivalent is typically used or a reasonably
   equivalent value or approximate conversion is used. It shall be
   acceptable to use the exact conversion or the conversions stated in
   the standard, even though they might not be exact.

    And the annex goes on to say:

   A.1.6.3 Some dimensions used in this standard require a tight
   precision and others do not. For example, when performing
   hydraulic calculations more precision is required than when
   specifying a nominal dimension. An example is pipe sizes, where we
   typically refer to a nominal diameter rather than the exact
   diameter. The metric equivalents also have a set of generally
   accepted nominal measurements, and they are not a precise conversion
   from the “English Unit” nominal dimension. Throughout the standard
   the generally accepted nominal pipe sizes have been used. For
   example 1 in. pipe = 25 mm, 11⁄4 in. pipe = 32 mm, 11⁄2 in. pipe =
   40 mm, and so forth. In other cases, rounding is used and the number
   of significant digits taken into account. For example, a 30 ft
   ceiling would be 9.144 m. This implies a level of precision that is
   higher than used for the original dimension, and a conversion to 9.1
   m or even 9 m is more appropriate. Another example is that in the
   standard, 1 in. has been converted to 25 mm and not 25.4 mm, 2 in.
   to 50 mm, 6 in. to 150 mm, and so forth. Finally, locally available
   material can have different characteristics in countries that use
   metric units than are typically found in the United States. Examples
   are things like standard door or window sizes, rack dimensions, and
   so forth. In these cases an approximate  conversion can also be
   used. Where approximate conversions have been used, it is acceptable
   for a designer or installer to use an exact conversion rather than
   the approximate conversion used in the standard.

I wasn't a part of it however memory serves to tell me there was a substantial metric conversion task group for this cycle.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 04/20/2016 3:42 PM, James Crawford wrote:
NFPA #13 (2013) section 8.12.3.2 minimum distance between ESFR heads not
less than 8’-0” or (2.4 m)

We are looking at a project and the ESFR heads are space at 2.4 meters apart
and this seems to meet code, but 2.4 m equals 7’-10 ½”.

Is this an over site by NFPA or are you allowed to be less than 8’-0” or
should it be 2.439 m and was just missed in the conversion.

This would be the same for the obstruction rule 1’-0” is 0.305 m not 0.3 m
and 2’-0” is 0.610 m not 0.60 m

Just wondering.

Thank you

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to