IFC 2012. 901.8 Pump and riser room size. Fire pump and automatic sprinkler system riser rooms shall be designed with adequate space for all equipment necessary for the installation, as defined by the manufacturer, with sufficient working room around the stationary equipment. Clearances around equipment to elements of permanent construction, including other installed equipment and appliances, shall be sufficient to allow inspection, service, repair or replacement without removing such elements of permanent construction or disabling the function of a required fire-resistance-rated assembly. Fire pump and automatic sprinkler system riser rooms shall be provided with a door(s) and unobstructed passageway large enough to allow removal of the largest piece of equipment.
Captain Frank J. Herrick City of Leawood Fire Department ________________________________________ From: Mike Stossel [[email protected]] Sent: Thursday, May 12, 2016 9:48 AM To: [email protected] Subject: Fire Pump Panel Can anyone confirm the clear space required in front of a fire pump panel? In NFPA 70 it appears to be 3”0”, but I would like to confirm that before I tell the client their room is too small. Thanks, [cid:[email protected]] Mike Stossel SET NICET Level IV Automatic Sprinkler System Layout 1070 38th Street Brooklyn N.Y. 11219 Office: 718-633-3036 ext 114 Fax: 718-633-4593 [email protected]<mailto:[email protected]> www.safetyfiresprinkler.com<mailto:[email protected]>