IN the 2015 IBC it is in 903.3.8 - Limited Area Sprinkler Systems

Limited to 6 sprinklers protecting either LH or OH / valve not required but if 
one is provided it must be electrically supervised / must calculate the 
sprinkler AND INCLUDE SIMULTANEOUS DOMESTIC DEMAND.

You probably also have to have a back flow preventer but the way it is written 
makes it debatable.

Other than that, easy peasy.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On Jun 1, 2016, at 2:56 PM, Jay White <[email protected]> wrote:
> 
> Where can I find code requirements for a single sprinkler being fed from a 
> domestic water line? Is it allowed? The application would be a bathroom at a 
> outdoor pool. Bathroom is detached and separate from main hotel building. 
> There is a domestic line supplying water to bathroom. Any information would 
> be appreciated.
>  
>  
> Jay White