IN the 2015 IBC it is in 903.3.8 - Limited Area Sprinkler Systems Limited to 6 sprinklers protecting either LH or OH / valve not required but if one is provided it must be electrically supervised / must calculate the sprinkler AND INCLUDE SIMULTANEOUS DOMESTIC DEMAND.
You probably also have to have a back flow preventer but the way it is written makes it debatable. Other than that, easy peasy. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Jun 1, 2016, at 2:56 PM, Jay White <[email protected]> wrote: > > Where can I find code requirements for a single sprinkler being fed from a > domestic water line? Is it allowed? The application would be a bathroom at a > outdoor pool. Bathroom is detached and separate from main hotel building. > There is a domestic line supplying water to bathroom. Any information would > be appreciated. > > > Jay White > Design Manager > Dynamic Fire Protection > 9771 Highway 25 South > Starkville, MS 39759 > PH: 662-312-2426 > FAX: 662-324-1545 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > <mailto:[email protected]> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>