Probably on the back flow device and probably in the state or
jurisdictional health code.

On Thursday, June 2, 2016, Roland Huggins <[email protected]>
wrote:

> IN the 2015 IBC it is in 903.3.8 - Limited Area Sprinkler Systems
>
> Limited to 6 sprinklers protecting either LH or OH / valve not required
> but if one is provided it must be electrically supervised / must calculate
> the sprinkler AND INCLUDE SIMULTANEOUS DOMESTIC DEMAND.
>
> You probably also have to have a back flow preventer but the way it is
> written makes it debatable.
>
> Other than that, easy peasy.
>
> Roland
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
> On Jun 1, 2016, at 2:56 PM, Jay White <[email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:
>
> Where can I find code requirements for a single sprinkler being fed from a
> domestic water line? Is it allowed? The application would be a bathroom at
> a outdoor pool. Bathroom is detached and separate from main hotel building.
> There is a domestic line supplying water to bathroom. Any information would
> be appreciated.
>
>
> *Jay White*
> *Design Manager*
> *Dynamic Fire Protection*
> *9771 Highway 25 South*
> *Starkville, MS 39759*
> *PH:   662-312-2426*
> *FAX: 662-324-1545*
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>

-- 
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to