You could. But you will lose the QR reduction due to unprotected ceiling 
pockets. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jun 10, 2016, at 7:05 AM, Dewayne Martinez 
> <[email protected]> wrote:
> 
> NFPA 13 (07ed), light hazard
>  
> I have an area with a bunch of rooms that are 14’x14’ with a ceiling at 14ft 
> elevation and a 7’x7’ “pedestal cloud” in the middle of the room at 12ft 
> elevation.  The cloud will be attached to the upper ceiling with a pedestal 
> base that will act as a wall to the any sprinklers in the high ceiling.   Can 
> I apply the ceiling pocket (8.6.7) or change in ceiling elevation  
> (8.6.4.1.1.3) and only put one head in the rooms in the lower cloud?  
> Otherwise I would need 3 heads and that seems like overkill.
> Thanks,
> Dewayne
>  
>  
>                                   