You could. But you will lose the QR reduction due to unprotected ceiling pockets.
Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Jun 10, 2016, at 7:05 AM, Dewayne Martinez > <[email protected]> wrote: > > NFPA 13 (07ed), light hazard > > I have an area with a bunch of rooms that are 14’x14’ with a ceiling at 14ft > elevation and a 7’x7’ “pedestal cloud” in the middle of the room at 12ft > elevation. The cloud will be attached to the upper ceiling with a pedestal > base that will act as a wall to the any sprinklers in the high ceiling. Can > I apply the ceiling pocket (8.6.7) or change in ceiling elevation > (8.6.4.1.1.3) and only put one head in the rooms in the lower cloud? > Otherwise I would need 3 heads and that seems like overkill. > Thanks, > Dewayne > > > > ___________________________________________________________________ > | > > | > | > > | > ____ > |____________________________________|______ > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org