Ceiling height needs to be the Highest point within Storage area(example I have
is 2/12 pitch roof)
25'6" will have a different psi starting PSIthan 24'6"just taking a quick
glance,using NFPA 13 2013 edtiontable 17.2.3.1 may get a starting point.
On Thursday, June 23, 2016 6:27 AM, Todd Williams <[email protected]>
wrote:
I am working on a location with existing K25 ESFR sprinklers. This is an
existing building where a new client is moving in. The ceiling height is
approximately 25 ft and there will be rack storage of plastics (both expanded
and unexpanded) to 20 ft. Looking through the chart in 13, there are some
section (the ones I am interested in) that only include 14.0 and 16.8. Any
particular reason why K25s aren't listed in these situations?
Todd G Williams, PEFire Protection Design/ConsultingStonington, CT860-535-2080
(ofc)860-608-4559 (cell)
Sent using CloudMagic