I’d look at whether it qualifies for the room design method (since dwellings 
units are separated by fire rated construction but the protection of openings 
poses a question).


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On Jul 5, 2016, at 12:34 PM, Bob <[email protected]> wrote:
> 
> I have a NFPA 13 building with Dwelling Units.  They each have three 
> Residential Sprinklers.  13 requires a four head calc.  Can I calc the 3 
> residential sprinklers and pick up one QR sprinkler in the corridor and still 
> satisfy the 4 head requirement?  Or, should I pick up one residential 
> sprinkler from an adjacent dwelling room?
>  
> Thank you,
>  
> Bob Knight, CET III
> 208-318-3057
> 
>  