WI, I haven’t done a residential project in some time. The building is concrete floors with non-combustible framing so maybe that makes the difference.
*From:* Sprinklerforum [mailto: [email protected]] *On Behalf Of *Steve Leyton *Sent:* Wednesday, July 06, 2016 2:04 PM *To:* [email protected] *Subject:* RE: Dwelling Unit Sprinkler Calc What state is that? In CA, you have to have one-hour between dwelling units. SL *From:* Sprinklerforum [ mailto:[email protected] <[email protected]>] *On Behalf Of *Dewayne Martinez *Sent:* Wednesday, July 06, 2016 11:49 AM *To:* [email protected] *Subject:* RE: Dwelling Unit Sprinkler Calc I would watch out on this. I am designing a high rise right now that the builder states the only fire rated walls per floor are the common corridor walls. I asked if the walls between the units will be rated and he said no. *From:* Sprinklerforum [mailto: [email protected]] *On Behalf Of *Roland Huggins *Sent:* Wednesday, July 06, 2016 12:55 PM *To:* [email protected]; [email protected] *Subject:* Re: Dwelling Unit Sprinkler Calc I’d look at whether it qualifies for the room design method (since dwellings units are separated by fire rated construction but the protection of openings poses a question). Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Jul 5, 2016, at 12:34 PM, Bob <[email protected]> wrote: I have a NFPA 13 building with Dwelling Units. They each have three Residential Sprinklers. 13 requires a four head calc. Can I calc the 3 residential sprinklers and pick up one QR sprinkler in the corridor and still satisfy the 4 head requirement? Or, should I pick up one residential sprinkler from an adjacent dwelling room? Thank you, Bob Knight, CET III 208-318-3057 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org