All of this is from NFPA-13 but the system is per NFPA-13R, doesn't that make a 
difference since the goal is life safety and not protection of property?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Phillips
Sent: Thursday, July 07, 2016 11:24 AM
To: [email protected]
Subject: RE: Obstructions Below Sidewall Sprinklers

Its not required and explained by 8.10.7.1.5.2

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Cliff Whitfield
Sent: Thursday, July 07, 2016 11:21 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Obstructions Below Sidewall Sprinklers

How do you address the 12" wide space that the wall cabinet creates between the 
top of the base cabinets and the bottom of the wall cabinets?  It's not 
protected in either scenario.

Cliff

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Phillips
Sent: Thursday, July 07, 2016 11:15 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Obstructions Below Sidewall Sprinklers

The soffit would need to be flush with cabinet face  8.10.7.1.5.2 of NFPA 13 
2010 ed in my opinion.
Mark


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Thursday, July 07, 2016 11:06 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Obstructions Below Sidewall Sprinklers

Looking for some clarification on sidewall sprinklers; We have a residential 
project that has a recessed sidewall head in the kitchen wall located 18" above 
a kitchen cabinet, the cabinet projects out 12" from the wall. Is this 
acceptable or does a soffit need to be built above the cabinet to bring the 
face of the sprinkler flush with the face of the cabinet?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to