Per NFPA 13R (07ed) 6.8.1.5.3.6(C) you need to be at least 3ft above to not have to build a soffit. Can install the heads on another wall and eliminate the obstruction all together?
*From:* Sprinklerforum [mailto: [email protected]] *On Behalf Of *Brian Harris *Sent:* Thursday, July 07, 2016 10:27 AM *To:* [email protected] *Subject:* RE: Obstructions Below Sidewall Sprinklers All of this is from NFPA-13 but the system is per NFPA-13R, doesn’t that make a difference since the goal is life safety and not protection of property? *Brian Harris, CET* BVS Systems Inc. bvssytemsinc.com <http://bvssystemsinc.com/> *From:* Sprinklerforum [ mailto:[email protected] <[email protected]>] *On Behalf Of *Mark Phillips *Sent:* Thursday, July 07, 2016 11:24 AM *To:* [email protected] *Subject:* RE: Obstructions Below Sidewall Sprinklers Its not required and explained by 8.10.7.1.5.2 *From:* Sprinklerforum [ mailto:[email protected] <[email protected]>] *On Behalf Of *Cliff Whitfield *Sent:* Thursday, July 07, 2016 11:21 AM *To:* [email protected] *Subject:* RE: Obstructions Below Sidewall Sprinklers How do you address the 12” wide space that the wall cabinet creates between the top of the base cabinets and the bottom of the wall cabinets? It’s not protected in either scenario. Cliff *From:* Sprinklerforum [ mailto:[email protected] <[email protected]>] *On Behalf Of *Mark Phillips *Sent:* Thursday, July 07, 2016 11:15 AM *To:* [email protected] *Subject:* RE: Obstructions Below Sidewall Sprinklers The soffit would need to be flush with cabinet face 8.10.7.1.5.2 of NFPA 13 2010 ed in my opinion. Mark *From:* Sprinklerforum [ mailto:[email protected] <[email protected]>] *On Behalf Of *Brian Harris *Sent:* Thursday, July 07, 2016 11:06 AM *To:* [email protected] *Subject:* Obstructions Below Sidewall Sprinklers Looking for some clarification on sidewall sprinklers; We have a residential project that has a recessed sidewall head in the kitchen wall located 18” above a kitchen cabinet, the cabinet projects out 12” from the wall. Is this acceptable or does a soffit need to be built above the cabinet to bring the face of the sprinkler flush with the face of the cabinet? *Brian Harris, CET* BVS Systems Inc. Sprinkler Division bvssystemsinc.com Phone: 704.896.9989 Fax: 704.896.1935
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org