2010 edition. This rule is for actiavation so it is the position of the bulb that matters, not the deflector orientation, just my two cents.
Brad On Jul 18, 2016 2:35 PM, "Parsley Consulting" <parsleyconsult...@cox.net> wrote: > Taylor, > perhaps expanding on Ryan's comment, it doesn't appear to me that it > would be applicable as the EC HSW above is not governed by anything in > section 8.8, rather it's covered in 8.9, and there's nothing in 8.9 or its > annex which matches the diagrams you referred to in 8.8. > Count my vote as saying it has no impact. > > *Ken Wagoner, SET Parsley Consulting* > > > > * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone > 760-745-6181 <760-745-6181> Visit our website > <http://www.parsleyconsulting.com/> * > On 07/18/2016 12:22 PM, Taylor Schumacher wrote: > > I understand that, but, the head making up the distance to the high head > is still a pendent. Just curious why this couldn’t apply to the type of > arrangement I’m proposing. > > > > *TAYLOR SCHUMACHER, CET* > > Security Fire Sprinkler > > *P* 320.656.0847 | *F* 320.656.0312 | *E* tay...@sfsprinkler.com > > > > *From:* Sprinklerforum [ > mailto:sprinklerforum-boun...@lists.firesprinkler.org > <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Ryan > Labrie > *Sent:* Monday, July 18, 2016 1:30 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* RE: Changes in Ceiling Elevation > > > > I would say no. 8.8 is rules for “Extended Coverage Upright and Pendent > Spray Sprinklers”. > > > > *Ryan Labrie* > > Fire Protection Designer > > > > > *Critical System Solutions, LLC *2830 Scherer Drive, Suite 300 > St. Petersburg, FL 33716 > Office: 727.209.5122 > > Fax: 727.209.5126 > > Cell: 813.394.3978 > > Email: rlab...@criticalsystemsolutions.com > > > > [image: CSS Logo] > > > > *From:* Sprinklerforum [ > mailto:sprinklerforum-boun...@lists.firesprinkler.org > <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Taylor > Schumacher > *Sent:* Monday, July 18, 2016 2:22 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* Changes in Ceiling Elevation > > > > Can the rules of NFPA 13, 2013 ed., 8.8.4.1.1.4(B)-see also Figure > A.8.8.4.1.1.4(A) be applied where the low sprinkler is a pendant in a > soffit and the high sprinkler is a sidewall? > > > > It reads “Where the distance between the upper ceiling and the sprinkler > deflector is less than or equal to 36 in., the sprinklers shall be > permitted to be spaced as though the ceiling were flat, provided the > obstruction rules and ceiling pocket rules are observed.” > > > > *TAYLOR SCHUMACHER, CET* > > Security Fire Sprinkler > > *P *320.656.0847 | * F * 320.656.0312 | *E *tay...@sfsprinkler.com > > > > > _______________________________________________ > Sprinklerforum mailing > listSprinklerforum@lists.firesprinkler.orghttp://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > >
_______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org