2010 edition.

This rule is for actiavation so it is the position of the bulb that
matters, not the deflector orientation, just my two cents.

Brad
On Jul 18, 2016 2:35 PM, "Parsley Consulting" <parsleyconsult...@cox.net>
wrote:

> Taylor,
>     perhaps expanding on Ryan's comment, it doesn't appear to me that it
> would be applicable as the EC HSW above is not governed by anything in
> section 8.8, rather it's covered in 8.9, and there's nothing in 8.9 or its
> annex which matches the diagrams you referred to in 8.8.
>     Count my vote as saying it has no impact.
>
> *Ken Wagoner, SET Parsley Consulting*
>
>
>
> * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone
> 760-745-6181 <760-745-6181> Visit our website
> <http://www.parsleyconsulting.com/> *
> On 07/18/2016 12:22 PM, Taylor Schumacher wrote:
>
> I understand that, but, the head making up the distance to the high head
> is still a pendent. Just curious why this couldn’t apply to the type of
> arrangement I’m proposing.
>
>
>
> *TAYLOR SCHUMACHER, CET*
>
> Security Fire Sprinkler
>
> *P*  320.656.0847  |  *F*  320.656.0312  |  *E*  tay...@sfsprinkler.com
>
>
>
> *From:* Sprinklerforum [
> mailto:sprinklerforum-boun...@lists.firesprinkler.org
> <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Ryan
> Labrie
> *Sent:* Monday, July 18, 2016 1:30 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: Changes in Ceiling Elevation
>
>
>
> I would say no. 8.8 is rules for “Extended Coverage Upright and Pendent
> Spray Sprinklers”.
>
>
>
> *Ryan Labrie*
>
> Fire Protection Designer
>
>
>
>
> *Critical System Solutions, LLC *2830 Scherer Drive, Suite 300
> St. Petersburg, FL  33716
> Office: 727.209.5122
>
> Fax:      727.209.5126
>
> Cell:     813.394.3978
>
> Email:  rlab...@criticalsystemsolutions.com
>
>
>
> [image: CSS Logo]
>
>
>
> *From:* Sprinklerforum [
> mailto:sprinklerforum-boun...@lists.firesprinkler.org
> <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Taylor
> Schumacher
> *Sent:* Monday, July 18, 2016 2:22 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Changes in Ceiling Elevation
>
>
>
> Can the rules of NFPA 13, 2013 ed., 8.8.4.1.1.4(B)-see also Figure
> A.8.8.4.1.1.4(A) be applied where the low sprinkler is a pendant in a
> soffit and the high sprinkler is a sidewall?
>
>
>
> It reads “Where the distance between the upper ceiling and the sprinkler
> deflector is less than or equal to 36 in., the sprinklers shall be
> permitted to be spaced as though the ceiling were flat, provided the
> obstruction rules and ceiling pocket rules are observed.”
>
>
>
> *TAYLOR SCHUMACHER, CET*
>
> Security Fire Sprinkler
>
> *P  *320.656.0847  | * F * 320.656.0312  |  *E  *tay...@sfsprinkler.com
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing 
> listSprinklerforum@lists.firesprinkler.orghttp://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>