There we go... the justification for the horizontally mounted pendants.
Thank you!


On Wed, Aug 10, 2016 at 11:11 AM, Don Casey <[email protected]>
wrote:

>
>
> Heads get used in ways they haven’t been listed in multiple scenarios.
>
>
>
> One easy one is for protecting steel columns when working with NFPA 15.
> I’ve used both pens and sidewalls depending on the configuration.
>
>
>
> In a duct, we’re typically looking to dump a certain amount of water into
> the duct which can be achieved using a sidewall or a pendant.
>
>
>
> Side note: a pen in a vertical duct  would not be installed per it’s
> listing and in a horizontal duct, it won’t meet the obstruction rules
> unless the duct diameter was greater than 18inches.
>
>
>
> As long as you can calculate the head(s) to deliver/operate at the
> flows/pressures stated by the applicable Standard (13 or 33 in this case)
> and is designed to operate at the minimum pressure as specified by the
> head’s listing (okay….not likely to come into play unless you wanted to use
> a K25 head and even then).
>
>
>
> Lastly, if you’re a stamping professional, you can come up with any design
> you think will work (which you’ve presumably based on data, experience,
> calculations, etc.).
>
>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *[email protected]
> *Sent:* 2016/08/10 1:46 PM
>
> *To:* [email protected]
> *Subject:* RE: Paint spray application
>
>
>
> Ductwork is like protecting specialty equipment, there isn’t necessarily a
> box you can put it in when it comes to NFPA 13 occupancies.  You have to be
> able to analyze the process and determine the hazard before you can assign
> a protection scheme for things such as this.
>
>
>
> One additional tool in the designer’s toolbox is the FM Global data
> sheets.  NFPA 13 doesn’t always address every single possible protection
> scheme where a water based sprinkler would be beneficial.  If you have
> questions about a particular application you can refer to other recognized
> industry Standards for additional information and insight.
>
>
>
> The owner doesn’t have to be FM insured to be able to use this data to
> defend or establish a design criteria for unique applications that NFPA may
> not address.  I have yet to run across an AHJ that rejected the use of FM
> Global criteria when NFPA didn’t address the situation.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Brad
> Casterline
> *Sent:* Wednesday, August 10, 2016 1:03 PM
> *To:* [email protected]
> *Subject:* RE: Paint spray application [EXTERNAL]
>
>
>
> Well, it's all I got.
>
>
>
> I think there is a little wiggle room regarding occupancy classification.
> For example, in the duct we can be max 12'-0" whilst outside the duct it is
> 10' max.
>
> That's a little weak, but, seeing as how I am a NICET certified
> engineering technician I see no wiggle room in using a sprinkler outside
> it's listing. I believe like you that deflector orientation in a duct is a
> non-issue due to deflectors determine the pattern at the floor, butt....
>
>
>
> see "Ken's well known aversion to courtrooms" for details :)
>
>
>
> Brad
>
>
>
> ps, thank you, and you too Bob, for helping me out of the doldrums
> yesterday
>
>
>
>
> ------------------------------
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *
> [email protected]
> *Sent:* Wednesday, August 10, 2016 7:44 AM
> *To:* [email protected]
> *Subject:* RE: Paint spray application
>
>
>
> How do you know the quantity of combustibles?
>
>
>
> Typically the issues with ductwork is based on a hazardous environment
> (transporting flammable or combustible vapors or combustible particulate)
> that’s the whole reason behind the requirement of protection of the
> ductwork.  The other condition is that there is accumulation of the same
> material on the interior of the duct over time creating a hazardous
> environment.
>
>
>
> So in either case there is no way to call it an ordinary hazard
> environment.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Brad
> Casterline
> *Sent:* Wednesday, August 10, 2016 8:40 AM
> *To:* [email protected]
> *Subject:* RE: Paint spray application [EXTERNAL]
>
>
>
> To be completely formal, is it possible to consider the duct to be an OH
> portion of the EH Classification? Not much quantity of combustible there.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to