Thanks, Glen -
So CPVC is ok and sprinklers are not needed in the truss space providing
there is no occupancy (13d & 13r).
Confusing, even though both of us can do hand calcs!
On 8/30/2016 2:22 PM, Glen Buelow, Inc. wrote:
Vince,
While figure a.9.1.1(a) shows it through the joist, the caution seems
to be what they are driving at. It can be run above joists if the
insulation can be secured to maintain protection.
*Glen Bue**low*
/Glen W. Buelow, Inc.
//Fire Protection Design and Consulting
Cleveland 330.220.7201 <tel:330.220.7201> /●/Akron 330.665.4439
<tel:330.665.4439>/
On Tue, Aug 30, 2016 at 1:38 PM, Vince Sabolik <[email protected]
<mailto:[email protected]>> wrote:
Good afternoon, forum.
We're looking at a redo of a 13D that had CPVC in the
unsprinklered trussed attic space under
the insulation but above the bottom chord.
OK or not?
I've read the manufacture's pamphlets - and well, depending on
which eye you want to close...
Anybody know for sure?
thanks, smart people -- Vince
11351 Pearl Road / Strongsville, Ohio 44136Phone 440 238-4800
<tel:440%20238-4800> Fax 440 238-4876 <tel:440%20238-4876>Cell 440
724-7601 <tel:440%20724-7601>
/Vince Sabolik /
_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
11351 Pearl Road / Strongsville, Ohio 44136Phone 440 238-4800 Fax 440
238-4876Cell 440 724-7601
/Vince Sabolik /
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org