Thank you. Some of the window pockets are 30-50 Ft. long but still under 1000 
Cu.Ft..

Old ceiling was 14 Ft. Drop ceiling is 10 Ft. It seems the volume should be the 
prime consideration not a 4Ft high pocket along an outside window wall.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of T. Silva
Sent: Tuesday, September 13, 2016 12:51 PM
To: [email protected]
Subject: Re: Ceiling Pockets



Skylights and similar pockets not exceeding 32 sq.ft. and separated from other 
pockets by minimum 10 feet do not require sprinklers. I would try to use that.

Tony

  _____

From: "Travis Mack" <[email protected]>
To: [email protected]
Sent: Tuesday, September 13, 2016 9:34:20 AM
Subject: Re: Ceiling Pockets

Just put a 2.8k sprinkler in the pocket. At least that minimizes the hydraulic 
impact to the system.

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone


On Sep 13, 2016, at 8:21 AM, Art Tiroly <[email protected]> wrote:

I have 4 Ft wide x 4 Ft deep window pockets in a 100 year old class room 
building with new drop ceilings.  Adding a sprinkler to a window pocket because 
it is over 3 Ft. deep makes no sense to me in these class rooms.   If a pocket 
sprinkler activates and washes the windows it does nothing for the fire 8-12 
Ft. away. I plan to ask for a variance from the Ohio State plans examiner at 
submittal though likely to no avail.



Art Tiroly

ATCO Fire Protection





From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Monday, September 12, 2016 5:51 PM
To: [email protected]
Subject: Re: Ceiling Pockets



It's all about activation Ron/Bruce.
Roland's insight as to the pass/fail criteria was a stroke of genius.

I like to explain it and then Roland corrects me. So I'll forego my part and 
wait for Roland to get his ears on.

Brad

On Sep 12, 2016 4:41 PM, "Bruce Verhei" <[email protected]> wrote:

Ron is briefer.


On Sep 12, 2016, at 14:39, Bruce Verhei <[email protected]> wrote:

Isn't the idea of using a Volume completely different than viewing his as an 
Area, such as a large sail sewing table that obstructs coverage as well as 
delaying operation?



Wasn't 1,000 cu ft a consensus guesstimate saying we'd allow a space this big 
for heat to accumulate in before banking down to activate heads? And experience 
presumably has shown it works, usually?



Putting a head to cover part of it is better if fire is under that head. If 
fire is away from head will you delay heat from banking down, resulting in a 
worse situation? I don't know. And I would guesstimate original designer 
doesn't either.



Best



Bruce Verhei


On Sep 12, 2016, at 11:21, T. Silva <[email protected]> wrote:


  _____


NFPA 13, 2013

8.6.7.2 (1) "The total volume of the unprotected ceiling pocket does not exceed 
1000 cu.ft."

Is the 1000 cuft only the volume of the pocket that is not sprinklered? For 
example, there is a pocket that is 30" long x 20' wide x 2' deep, creating a 
1200 cuft ceiling pocket. If one row of sprinklers are provided in this pocket 
(along the 30 foot length), to provide a protected area of 30' x 10'

(1) Is the the total volume of the unprotected ceiling pocket still 1200 cuft? 
or
(2) Reduced to 600 cuft, discounting the sprinklered area?

Thanks,

Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to