Sprinklers above the egg crate will have obstructed flow spray pattern.

How far below the deck are the sprinklers in the egg crate ceiling?

If more than 12"???

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of J.P. Merlino/Ing. L.Lagomarsino & Asoc.
Sent: Thursday, September 15, 2016 6:00 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Open-Grid Ceilings - Egg crate

 

Dear Sirs:

NFPA 13 Ed. 2016 - 8.15.14

If we have an open grid egg-crate that meets 70% open space but the depth of
the material (2 in) exceeds the least dimension (1 in) it does not comply
with the allowance not to install sprinkler beneath and we must install in
the egg-crate (or beneath).

But the standard is silent on what to do with the space over the egg-crate.
Shall we have two layers of sprinklers, one in the egg-crate and the other
over the egg-crate as if the egg-crate does not exist?

I appreciate your thoughts or if we are missing something.

best regards

J.P. Merlino



---