blockquote, div.yahoo_quoted { margin-left: 0 !important; border-left:1px 
#715FFA solid !important; padding-left:1ex !important; background-color:white 
!important; }  REHAU Had a complete line of fittings for installation of PEX 
fire sprinkler systems imbedded in concrete which is used in the UE.
It was used in systems beyond 13D. Check with them might be able to work 
something out with them. 
Mike C



Sent from Yahoo Mail for iPhone


On Friday, October 7, 2016, 11:25 AM, rongreenman . <[email protected]> 
wrote:

Isn't PEX used as the piping in heated floors where you would have a large 
change in temperature from winter (using it to halt the floor cum building, and 
summer where you wouldn't?

On Fri, Oct 7, 2016 at 6:31 AM, Steve Leyton <[email protected]> wrote:

I think an investigation of the potential for thermal expansion would be 
prudent. The applications I described topped with 3-8 feet of earth, so 
temperatures were stable year-round.  But PEX is designed to expand and 
contract without loss of structural integrity, so it's well suited for 
embedment in concrete.

Steve

-------- Original message --------From: Ben Young <[email protected]> 
Date: 10/7/16 6:27 AM (GMT-08:00) To: sprinklerforum@lists. firesprinkler.org 
Subject: Re: Monolithic domes 
I thought about PEX as well Steve, its no four letter word for me.  At least 
with the CPVC we can comply with the pipe requirements from NFPA 13, which 
would require less 'selling' than PEX use.  Although as Mark points out about 
thermal expansion, PEX does have a lower rate of I think about an inch per 100 
feet.  Because the concrete acts as a thermal sink and they are insulated on 
the outside, I think the temperatures inside are incredibly stable.  The 
Wikipedia page for these things makes them sound incredibly attractive for 
almost any building type, but there are some drawbacks.


I'm just really surprised at the complete and utter lack of information on 
sprinklering these except for the one I posted.


Benjamin Young

On Thu, Oct 6, 2016 at 10:41 PM, Steve Leyton <[email protected]> 
wrote:

Listed PEX A and I think the sprinklers were screwed right into the branch 
fittings because we only needed 30 minutes per UL 1821. If you really need the 
details, I have to look at my technical report and may not be able to do that 
for a couple days as I'm taking a long weekend.
Wine caves are a little different than overhead domes because we ran a CPVC 
main down the corridors under the floor and branched off with 1" PEX that 
wrapped halfway around the vault serving a single sprinkler. The CPVC was 
directly buried and the floors were made of hand-laid stone on a sand bed.
But I think you could drop to the sprinklers with CPVC or even use PEX because 
I'm not as worried about protecting piping that has a sprinkler between it and 
the heat source as I might be concerned about a piping span that's between 
sprinklers.
Steve

-------- Original message --------From: AKS-Gmail-IMAP 
<[email protected]>Date: 10/6/16 7:23 PM (GMT-08:00) To: 
[email protected] kler.org Subject: Re: Monolithic domes 
If I may ask, was that PEX A or B and how were the last bit of drop piping 
handled where the sprinklers screwed in?
Allan SeidelSt. Louis, MO


On Oct 6, 2016, at 3:32 PM, Steve Leyton <[email protected]> wrote:
It’s a dirty word on this Forum to some, but I would consider looking into PEX 
tubing if you can get it to work hydraulically.  The challenges with PEX are 
smaller ID and temp/pressure rating.   However, PEX can easily be attached to 
the formwork for concrete or Gunnite and we have used it with great success in 
wine caves out here on the Left Side.    Aggregate concrete has a fire 
resistance rating that can be extrapolated as about 22.2 minutes per inch and 
I’ve done tech reports for two wine cave applications where we obtained 
equivalency approval for this application.    Steve Leyton  From: 
Sprinklerforum [mailto:sprinklerforum-bounces @lists.firesprinkler.org] On 
Behalf Of Maurice Marvi
Sent: Thursday, October 06, 2016 12:58 PM
To: [email protected] prinkler.org
Subject: re: Monolithic domes Repairing buried CPVC branch lines sounds like 
fun. Not. 
Maurice Marvi

From: "Ben Young" <[email protected]>
Sent: Thursday, October 06, 2016 3:18 PM
To: "[email protected] nkler.org" <[email protected] 
nkler.org>
Subject: Monolithic domes

Does anyone have any information at all about putting sprinklers in a concrete 
monolithic dome?

I was able to find one article about it at the monolithic dome institute's 
website here:
http://static.monolithic.com/c onstruction/sprinklers/index.h tml
Looks crazy, but also interesting.

Benjamin Young ______________________________ _________________
Sprinklerforum mailing list
[email protected] kler.org
http://lists.firesprinkler.org /listinfo.cgi/sprinklerforum- firesprinkler.org


______________________________ _________________
Sprinklerforum mailing list
[email protected] kler.org
http://lists.firesprinkler.org /listinfo.cgi/sprinklerforum- firesprinkler.org




______________________________ _________________
Sprinklerforum mailing list
Sprinklerforum@lists. firesprinkler.org
http://lists.firesprinkler. org/listinfo.cgi/ sprinklerforum-firesprinkler. org





-- 
Ron Greenman
4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to