What is the reasoning for the 4” minimum space to a wall or duct? It isn’t activation or spray pattern since sidewall sprinklers operate in a recessed escutcheon.
Art at ATCO Fire From: Sprinklerforum [mailto:[email protected]] On Behalf Of rongreenman . Sent: Wednesday, October 19, 2016 5:32 PM To: [email protected] Subject: Re: Sprikler obstruction. For standard spray sprinklers: 4" from the duct unless a sidewall (you could use a vertical type) and no closer the 6' from the next closest sprinkler. The rules are pretty clear. Unless you can find a sprinkler who's listing negates these rules you're stuck. On Wed, Oct 19, 2016 at 2:26 PM, Art Tiroly <[email protected] <mailto:[email protected]> > wrote: 12x16” Duct is tight to ceiling. Up right Sprinkler is about 6” from ceiling on exposed pipe. Fire Marshall’s issue is that the sprinkler is about 2.5” from the face of the duct. Adjacent sprinkler is about 6’-0 away. Art From: Sprinklerforum [mailto:[email protected] <mailto:[email protected]> ] On Behalf Of Cesar Lira Sent: Wednesday, October 19, 2016 4:20 PM To: [email protected] <mailto:[email protected]> Subject: RE: Sprikler obstruction. What size is the duct and what is the distance between the sprinkler and the top of duct. De: Sprinklerforum [mailto:[email protected]] En nombre de IPA Enviado el: miércoles, 19 de octubre de 2016 02:02 p. m. Para: [email protected] <mailto:[email protected]> Asunto: Re: Sprikler obstruction. Is the duct below the sprinkler deflector? On Wed, Oct 19, 2016 at 12:25 PM, Art Tiroly <[email protected] <mailto:[email protected]> > wrote: Does an upright sprinkler have to be moved when a new duct was added less than 4” away from the existing sprinkler. I understand when a new sprinkler is installed it shall be 4” away from a wall. I have adequate coverage from the adjacent sprinkler in this basement meeting room space. Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 <tel:216-621-8899> 216-570-7030 <tel:216-570-7030> cell _____ <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> This email has been checked for viruses by Avast antivirus software. www.avast.com <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> _______________________________________________ Sprinklerforum mailing list [email protected] <mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _____ <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> This email has been checked for viruses by Avast antivirus software. www.avast.com <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> _______________________________________________ Sprinklerforum mailing list [email protected] <mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Ron Greenman 4110 Olson Dr., NW Gig Harbor, WA 98335 [email protected] <mailto:[email protected]> 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-)
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org