What is the reasoning for the 4” minimum space to a wall or duct?

It isn’t activation or spray pattern since sidewall sprinklers operate in a 
recessed escutcheon.

 

Art at ATCO Fire

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Wednesday, October 19, 2016 5:32 PM
To: [email protected]
Subject: Re: Sprikler obstruction.

 

For standard spray sprinklers: 4" from the duct unless a sidewall (you could 
use a vertical type) and no closer the 6' from the next closest sprinkler. The 
rules are pretty clear. Unless you can find a sprinkler who's listing negates 
these rules you're stuck.

 

On Wed, Oct 19, 2016 at 2:26 PM, Art Tiroly <[email protected] 
<mailto:[email protected]> > wrote:

12x16” Duct is tight to ceiling.

Up right Sprinkler is about 6” from ceiling on exposed pipe.

Fire Marshall’s issue is that the sprinkler is about 2.5” from the face of the 
duct.

Adjacent sprinkler is about 6’-0 away.

 

Art

 

From: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of Cesar 
Lira
Sent: Wednesday, October 19, 2016 4:20 PM
To: [email protected] 
<mailto:[email protected]> 
Subject: RE: Sprikler obstruction.

 

What size is the duct and what is the distance between the sprinkler and the 
top of duct.

 

 

De: Sprinklerforum [mailto:[email protected]] En 
nombre de IPA
Enviado el: miércoles, 19 de octubre de 2016 02:02 p. m.
Para: [email protected] 
<mailto:[email protected]> 
Asunto: Re: Sprikler obstruction.

 

Is the duct below the sprinkler deflector?

 

 

On Wed, Oct 19, 2016 at 12:25 PM, Art Tiroly <[email protected] 
<mailto:[email protected]> > wrote:

Does an upright sprinkler have to be moved when a new duct was added less than 
4” away from the existing  sprinkler.

I understand when a new sprinkler is installed it shall be 4” away from a wall.

I have adequate coverage from the adjacent sprinkler in this basement meeting 
room space.

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899 <tel:216-621-8899> 

216-570-7030 <tel:216-570-7030>  cell

 

 

  _____  


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 

This email has been checked for viruses by Avast antivirus software. 
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
  

 


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

 

  _____  


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 

This email has been checked for viruses by Avast antivirus software. 
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
  

 


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





 

-- 

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected] <mailto:[email protected]> 

253.576.9700

 

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to