Thank you.

Does the same effect occur next to a duct we wonder.

The ceiling area forms a pocket that is 4’ from an adjacent wall 4Ft away to 
sprinkler that is next to a duct.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Thursday, October 20, 2016 4:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.



>From the 1984 Technical Committee Reports for Proposal 13-401:



“SUBSTANTIATION Guidance is needed for the placement of standard sprinklers (ie 
non sidewall heads) in relation to their horizontal proximity to walls. Dead 
air spaces in corners can effect a sprinkler’s operation time. The minimum 
clearance for sidewall was used (NFPA 13  4-5.4). A recent installation in a 
300 ft long by 9 ft wide corridor caused this concern when the sprinklers were 
located only 1 in off the wall.”



Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: October-20-16 9:42 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.



What is the reasoning for the 4” minimum space to a wall or duct?

It isn’t activation or spray pattern since sidewall sprinklers operate in a 
recessed escutcheon.



Art at ATCO Fire







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Wednesday, October 19, 2016 5:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprikler obstruction.



For standard spray sprinklers: 4" from the duct unless a sidewall (you could 
use a vertical type) and no closer the 6' from the next closest sprinkler. The 
rules are pretty clear. Unless you can find a sprinkler who's listing negates 
these rules you're stuck.



On Wed, Oct 19, 2016 at 2:26 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

12x16” Duct is tight to ceiling.

Up right Sprinkler is about 6” from ceiling on exposed pipe.

Fire Marshall’s issue is that the sprinkler is about 2.5” from the face of the 
duct.

Adjacent sprinkler is about 6’-0 away.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cesar Lira
Sent: Wednesday, October 19, 2016 4:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.



What size is the duct and what is the distance between the sprinkler and the 
top of duct.





De: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] En 
nombre de IPA
Enviado el: miércoles, 19 de octubre de 2016 02:02 p. m.
Para: sprinklerforum@lists.firesprinkler.org
Asunto: Re: Sprikler obstruction.



Is the duct below the sprinkler deflector?





On Wed, Oct 19, 2016 at 12:25 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

Does an upright sprinkler have to be moved when a new duct was added less than 
4” away from the existing  sprinkler.

I understand when a new sprinkler is installed it shall be 4” away from a wall.

I have adequate coverage from the adjacent sprinkler in this basement meeting 
room space.



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell





  _____


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 Imagen quitada por el remitente. Avast logo

This email has been checked for viruses by Avast antivirus software.
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>




_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





  _____


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 Image removed by sender. Avast logo

This email has been checked for viruses by Avast antivirus software.
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>




_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org







--

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com

253.576.9700



The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)



---